I have (2) 5 HP single phase, dual stage air compressors. When they are both running I notice slight flickering in smaller wattage (60W) incandescent and fluorescent light bulbs. If only one is running the flickering is almost unnoticeable. Using a Fluke 325, I measured motor current and they read 23A before they stop which is nameplate. Voltage at the main panel drops about 2V for each running compressor. Starts at 246V, drops to 244V with one compressor running, and drops to 242V with both running. At the magnetic starter, I am reading 239V. Wire is 50 foot of #10 all the way to the motor. Lights do not dim excessively when they start, not really any more than when the air conditioner starts. While running, voltage at the panel between hot and neutral is about 121-122 and does not bounce around. Panel is 100A. Neighbors say they don't see any flicker. Any ideas as to why the lights have the slight flicker and if there's anything I can do about it?