This guy has a pretty simple setup with his Takagi, this might be the winner coming in less than $2k
Don't follow him .........
Pumping away is correct for a cast boiler -- or other higher mass boiler. even a lower mass floor copper boiler. It is not correct for a wall type boiler or on demand hot water heater.
Wall hung use primary/ secondary -- due to the type of heat exchanger they have
He has mixed it all up. If you look at the manual for the heater you will see the diagram shows the pump -- pumping into the unit -- this is typical and required to overcome the high resistance of the internal heat exchanger. Remember hot water heaters are expecting high pressure from your house water supply to the cold inlet. They are also intended for higher output -- that's why you see them connected to hydroair. All of the manufacturers units that are able to be used for any type of domestic heating have it that way.
Anyway .... even on low fire at 18k --- it's a very big boiler and will have to go on and off. Since it's really designed to heat water for domestic use -- the input is very large.
He is getting enough flow because his pump is huge .... way bigger than required ..... wonder what is the power usage. All said he is only getting 1.3gpm. Not much given the pump. Radiant is very forgiving -- if you pump heat into a slab .... it will get hot and heat the space.
As far as the controls -- he is doing a manual control. Picking the temp of the boiler water and using the air temp in the space to regulate the final temp. This could all be done with outdoor reset -- the boiler changes temp of water based on outside temp and it's automaic. You would have to find the cheapest unit with it ....
The little book I referenced about primary/ secondary -- the author is the same person who wrote "pumping away" . The guy in the video just did not know that his boiler is not the same. The fluid engineering and principles/ laws are all now on the secondary with a wall boiler .... not as he has done them on the primary.
Also with new pumps -- they have internal check valves. No need to add aditional types and you don;t use swings. Using my recommended fitting on the spriovent eliminates some of his mess -- and you have a pressure gauge right there. Also ---- his tank is too big. Look at the tank in mine w/ thousands of feet of PEX ... the little red one.
All the videos on the internet have been wrong IMO ....