I am configuring lighting for the shop.
I have 22 hanging florescent fixtures. The plug in type. They read 120 volt.
Each has two 30 watt T8 bulbs.
I thought I would be fine with one 120 volt 20 amp breaker, 12 gauge wire and 20 amp reciprocals across the 14' ceiling.
20 amps x 120 volts x 80% puts me at 1920 watts. The 44 bulbs draws 1320 watts.
Then i see this sticker on the fixture which gives me pause....
If I multiple all my lamps according to this label it puts me at 3300 watts. Which would mean I will need an additional breaker. Correct?

I have 22 hanging florescent fixtures. The plug in type. They read 120 volt.
Each has two 30 watt T8 bulbs.
I thought I would be fine with one 120 volt 20 amp breaker, 12 gauge wire and 20 amp reciprocals across the 14' ceiling.
20 amps x 120 volts x 80% puts me at 1920 watts. The 44 bulbs draws 1320 watts.
Then i see this sticker on the fixture which gives me pause....
If I multiple all my lamps according to this label it puts me at 3300 watts. Which would mean I will need an additional breaker. Correct?