I replaced the ballast on a 23 year old basic fluorescent 2 tube 42" fixture.

[Fluorescent eBallast for 2 F40T12 Linear Lamps, Preheat- Rapid Start, 120Vac, 50-60Hz, Normal Ballast Factor, NPF]

When I apply power (120v) the light/tube ends glow but the light does not come on, however, if I touch the tubes it comes on...

Repeated several times.

Any help?

Or does this need to go to land fill:dunno:
 
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,759
Location
NW Iowa
Make sure the ballast and fixture are grounded. That makes a difference with rapid start ballasts, NPF (normal power factor) and LPF (low power factor) ballasts seem to be more prone to this issue than HPF (hig power factor).

Most of these ballast will actually have something to the effect of "mount lamps within 1/2" of grounded metal reflector" printed on the label.
 

BillK

Well-known member
Joined
Aug 24, 2006
Messages
9,349
Location
Beautiful Southern Maryland
Scratch,
Don't rule out a defective ballast. I replaced one at my shop about a year ago and had the same exact issue. Returned the ballast and got another one and the problem was fixed.
 

snyder

Well-known member
Joined
Dec 18, 2008
Messages
545
Location
Baltimore md.
Double check your wiring. Make sure the wires are
Clipped into the end caps securely. Check for burnt or broken tabs in the end caps. After that it could be a bad ballast.
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,905
I replaced the ballast on a 23 year old basic fluorescent 2 tube 42" fixture.

[Fluorescent eBallast for 2 F40T12 Linear Lamps, Preheat- Rapid Start, 120Vac, 50-60Hz, Normal Ballast Factor, NPF]

When I apply power (120v) the light/tube ends glow but the light does not come on, however, if I touch the tubes it comes on...

That's a sign the reflector isn't grounded. When the tube starts, a capacitor is formed between the tube wall and the reflector. Charging the capacitor causes current to flow, which ionizes some gas in the tube. That makes striking the arc easier. if the reflector isn't ground, you don't get the capacitance or the current flow, so the arc is harder to strike. Touching the tube forms a capacitor between your hand, and the inside of the tube wall, and lets the arc gets started.

Is there a reason you didn't use a t8 ballast? They, and t8 tubes, are more efficient.
 
To avoid these ads, REGISTER NOW!

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,313
Location
Dutzow Missouri
1 Did you say both lamps are new?

2 Do you really have a 42” fixture?

3 You will need a good ground connection from the electrical panel to the reflector.

4 Are the lamps you installed T12? T8s will be too far from the reflector.

5 Rapid start ballasts are 1950 technology. When they fail now is time to replace them with modern electronic ballasts. You will have lower electric bills, brighter lights and reliable start.


Walta
 
OP
S

scratchedup

Well-known member
Joined
Aug 13, 2012
Messages
834
Location
Fayetteville, GA
Fixture old...25+ years...
Tubes 48"- F34CW.RS.ECO
Tubes have been replaced but they are pretty old but still work.
Ballast off Amazon ~ $13.

Got up this morning are the thing seems to be working. I will set a ground wire. I think years ago I threw this up with out using the ground wire. The Nomex? power supply still has the bare ground wire unused.
 
OP
S

scratchedup

Well-known member
Joined
Aug 13, 2012
Messages
834
Location
Fayetteville, GA
This is the ballast-
ROBERTSON 3P20132 Fluorescent eBallast for 2 F40T12 Linear Lamps, Preheat- Rapid Start, 120Vac, 50-60Hz, Normal Ballast Factor, NPF, Model RSW234T12120 /A (Crosses to 3P20010 Model RSW240T12120 /B)
 

FTG-05

Well-known member
Joined
Oct 11, 2012
Messages
1,541
Location
TN
I would never replace a ballast on flor light fixture. Total waste of money that produces zero light in and of itself.

Instead, replace the flor light bulbs with LED ballast bypass bulbs.

Let's count the advantages:

- No more ballast = no more ballast failures
- Higher output and more efficient light i.e. +110 lumens/watt
- Instant on regardless of temps
- No more flickering or buzzing and no real possibility of either ever
- Cost? About the same as a new ballast +/-

Disadvantages:

- You have to rewire the light fixture; no real biggie unless you're a wiring virgin

Good luck.
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
10,989
Location
Rhode Island
This is the ballast-
ROBERTSON 3P20132 Fluorescent eBallast for 2 F40T12 Linear Lamps, Preheat- Rapid Start, 120Vac, 50-60Hz, Normal Ballast Factor, NPF, Model RSW234T12120 /A (Crosses to 3P20010 Model RSW240T12120 /B)

Rapid start ballasts really need the fixture or ballast to be grounded to start properly and reliably. There's a ground wire going to the fixture, hook it up.
 

cybrdyke

Well-known member
Joined
Sep 9, 2014
Messages
3,449
Location
USA
The ballast that you wanted has been discontinued for years. The 34 watt lamps that you used are likely not the same as the version that used to be out there. Your old ballast had no trouble firing them.
So now, you have old lamps that are reduced wattage (energy saving) and a ballast with a low ballast factor (.81).
They just dont work together very well. The new ballast hasn't got the voltage to fire the tubes completely. They'll start sometimes, other times not so much. Probably when you need them the most.
As was discussed above, either change the ballast to T8 Instant Start or bypass it entirely and use LED tubes.
Good luck,
CD
 