Do GFCI's not like flourescent lights? I installed a small (24") single-bulb 17W T8 corded fixture in my garage, plugged into a GFCI outlet. If I toggle the on/off rocker switch more than once the outlet trips. Thoughts?

Thanks,
Jeff
 
To avoid these ads, REGISTER NOW!
OP
M

mjeff87

Well-known member
Joined
Jan 22, 2010
Messages
2,752
Location
Richmond, VA
thanks Charles......I'll have to run it to a different outlet (which is nowhere close to the light:mad:)

Jeff
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
I have two 4' flo lights plugged into GFCI supplied outlets and never have any problems. I would change the ballast in the light or toss the light.
 
To avoid these ads, REGISTER NOW!
OP
M

mjeff87

Well-known member
Joined
Jan 22, 2010
Messages
2,752
Location
Richmond, VA
funny thing is, I just moved the light from above the workbench to the other side of the garage. Above the bench it was plugged into a regular outlet and worked without a problem, but it's not playing well with the GFCI. It is an older fixture, though....

Jeff
 

Gary S

Well-known member
Joined
Dec 27, 2008
Messages
2,972
Location
Bismarck, ND
It might be time to consider a different light fixture.
I have two 4' florescent lights with T8 lamps over my workbench. They are plugged into one of my GFI protected circuits and have never tripped the GFI.
 

Tom McDermott

Active member
Joined
Aug 29, 2008
Messages
36
Location
Oregon
Depends on the age of the GFCI. Older ones had several problems. UL changed the specifications in 2003 to reduce radio frequency interference susceptibility, false tripping, etc.; and again in 2006 to force them to trip when wired up with line an dload reversed.

Look for a replacement GFCI marked "Meets the requirements of UL2006" or some similar wording (or just plug into a non-GFCI outlet).

-- Tom
 
OP
M

mjeff87

Well-known member
Joined
Jan 22, 2010
Messages
2,752
Location
Richmond, VA
brand new house, I'm fairly certain the outlet meets current UL specs.

I pulled the flouro fixture and replaced it with a $20 xenon-bulb unit from Lowe's, and all is well. I'll keep the flouro to use on the ground when I'm working on the Heep:)

Thanks all!

Jeff
 