Hey everyone,

First post here, just joined up yesterday! I closed on my first home 4 months ago. I searched long and hard to find a house with an oversized garage, and I eventually found one with a double deep 2 bay detached garage measuring 26 x 34. Althought I have big plans for the garage, I have been focusing most of my efforts on the house up until this point unfortunately, but my father was able to get me 8 48" double tube fluorescent lights that they were going to be throwing out at his work. I want to put them up in my garage in place of the 8 incandescent sockets that are in there now (4 on each circuit). My question is, will I be in trouble in the winter with the florescent lights only? It can get pretty cold in NH, and the garage is detached and unheated. Will I have problems with the nights not starting at all, or will I just have to give them some time?

Thanks for the insight!
 
To avoid these ads, REGISTER NOW!

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,678
Location
Long Island
That depends on the fixture.
I've had some old T12 fixtures that would not light below 32F.
Some would just be really dim below 40F.
My experience with T12, is that if they don't start in the cold, they won't start no matter how long you wait.

A lot of T8 stuff will light down to -20F (some are just rated to start at 0F), and once the start, they will warm up to full brightness in a few minutes.

I'd say to try them if you really want to save a few bucks, but don't get your hopes up.
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
You'll want to change the ballasts to T8 electronic ballasts and you should have little trouble down into the teens or below. If they are T12 mag ballasts, forget it - use the fixtures and change the ballasts.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
The OP will need to tell us something about the light fixtures before we can offer much advice. Are they the large diameter T12 bulbs (1-½ inch diameter) or are they T8 bulbs (1" diameter) and do they have older magnetic ballasts (very heavy) or newer electronic ballast (very lightweight).

What kind of fixtures are they? open strips? Strips with reflectors? Oddball enclosed (wet location, explosion proof, etc). Pics of the fixtures and the data plates are very helpful.

Charles
 

shweppie

Member
Joined
Dec 12, 2012
Messages
7
Location
New Oxford, PA
Make sure those ballasts are 120/240v and not 277, considering they are from a commercial place im assuming. Just a thought and also def electronic T8 is the way to go. Ballast can be pretty costly and is almost worth just getting brand new fixtures.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,301
Location
SE MI
i converted my 277 t-12's to 120, the ballasts were like 30 bucks a piece it wasnt too horrendous

I bought new double T8's for less than $30 each at HD. They work fine down to 0F. Might take a minute to get to full brightness.

Even CFL floods work at 0F. They take a couple of minutes to get to full brightness.
 
OP
M

Mr. Roboto

Well-known member
Joined
Dec 11, 2012
Messages
2,161
Location
New Hampshire
Thanks for the replies. Sorry for the lack of info, I wasn't sure what info was relevant. I looked at the ballasts, they are Sylvania QTPx32T8/UNV 120V - So I'm assuming that means they are T8s? Which from what was stated above will be OK in the cold? Also the bulbs are 1" diameter 4100K.

Here is a picture of what the fixture looks like:

10131461.jpg


Thanks again!
 

amolaver

Well-known member
Joined
Mar 10, 2009
Messages
835
based on your description and the pic, looks like a great freebie. you'll want to actually look at the ballasts and confirm they are 120v (vs being converted to some more commercial power friendly voltage), but i'd say all signs look promising.

give the reflectors a good cleaning as it will make a big difference in the amount of light they throw, check the ballasts, and get 'em mounted and lamped. then, enjoy :)

ahm
 
OP
M

Mr. Roboto

Well-known member
Joined
Dec 11, 2012
Messages
2,161
Location
New Hampshire
Here is a picture of the ballast. It looks to be 120V to me, but will also accept up to 277? doesn't seem to be anything funky going on with them.

21086722.jpg
 
Last edited:

kbs2244

Well-known member
Joined
Nov 11, 2006
Messages
14,065
They are free.
Use them.
Even if slow you cannot go wrong.
If it was me though, I would keep the incandescent bulbs as well.
That will give you instant light as well a good over all.
 

vartz04

Well-known member
Joined
Feb 17, 2009
Messages
1,882
Location
LaSalle County IL
At 30 degrees in my garage the 3 T8 lights I have flick right on and are full brightness in about 2 minutes. (still plenty light to see around the garage) the 1 T12 that I "borrowed" from the basement takes a good 10 minutes to get full brightness and usually only one bulb comes on unless I flip the switch a couple times. Ill be replacing that one here in the next week or so.
 

geotek

Well-known member
Joined
Oct 4, 2011
Messages
158
Location
Troy, NY
They are free.
Use them.
Even if slow you cannot go wrong.
If it was me though, I would keep the incandescent bulbs as well.
That will give you instant light as well a good over all.

^^^^^^agreed you can never have too much light in a garage!
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,678
Location
Long Island
It says right on your ballast:
Min Start Temp 0F
A picture is worth 1000 words.

And that ballast is good for anywhere between 120V and 277V
Sounds like you will be fine. Just be sure to use T8 bulbs.

If you're paranoid, you could replace a couple of your ballasts with ones that start at -20F. That way, even in the coldest of days, you would get some light right when the switch turns on.

Anyway, you have nice fixtures, and congrats on the new garage. ;)
 
OP
M

Mr. Roboto

Well-known member
Joined
Dec 11, 2012
Messages
2,161
Location
New Hampshire
wow I am blind, I did not even see that it was listed on the ballast I'm sorry. For the time being I will just simply wire them in place of the incandescent lights, and see how this winter goes. Sounds like they will fire up no problem. Until I do something about the lack of heat/insulation in there, I don't see myself workout out there a whole lot anyways until the weather warms up.
 

Steve.S

Well-known member
Joined
Sep 25, 2011
Messages
1,661
Location
Cincinnati, Ohio
wow I am blind, I did not even see that it was listed on the ballast I'm sorry. For the time being I will just simply wire them in place of the incandescent lights, and see how this winter goes. Sounds like they will fire up no problem. Until I do something about the lack of heat/insulation in there, I don't see myself workout out there a whole lot anyways until the weather warms up.

Stick around here long enough and you'll be installing a furnace, bathroom, and mini-bar for use year-round! :lol_hitti
 

jvitez

Well-known member
Joined
Nov 30, 2009
Messages
2,429
Location
Big Sky Country, Canada
Keep the incandescent lights, but move them to give general illumination in the whole garage. Wire the fluorescents separately. When cold and just grabbing something from the garage you can flick on the incandescents. Put the fluorescents on a separate switch.
 
To avoid these ads, REGISTER NOW!

ChevyEFI

Well-known member
Joined
Sep 2, 2012
Messages
8,790
Location
Phoenix, AZ
I have a similar issue.

I have a 48" 2 bulb 120V fixture that 1) fails to fully light the bulbs fully when chilly (as it get below 50F or 10C) and 2) is rusty.

What's a better fixture option? Power use isn't a huge deal where it is (Laundry off the garage) and I enjoy not regularly replacing bulbs. T8 & T8 bulbs? Anything LED worthwhile?
 
OP
M

Mr. Roboto

Well-known member
Joined
Dec 11, 2012
Messages
2,161
Location
New Hampshire
To update this thread, I installed all of these lights this fall. They do NOT want to run very well at all in any weather below 40 degrees or so, despite the fact that they are T8 ballasts. They say "Max Start Temp: 0F" right on the ballasts, but this certainly is not the case. I turn them on and can barley see the ends of each bulb glowing, and that's about it.

Any idea what's going on? Could the ballasts or bulbs just be showing their age?

Thanks!
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
Get F96T8 ballasts for (2) bulb fixtures. I have (3) two bulb T8 8' fixtures in my garage with standard ballasts & standard bulbs. I got them used from work when we upgraded to T5HOs. They light right off even in 2 or 3* weather. If you REALLY have a cold start problem, just get a cold rated ballast...

Tommy
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Post #1 is where were went astray.

.... but my father was able to get me 8 48" double tube fluorescent lights that they were going to be throwing out at his work........

The OP described them as 48 inch (4 ft) and no one apparently caught the fact they were single pin, which is not made in anything other than an 8 ft length. I'm not familiar with 8 ft T8 so I don't know if it is single pin or not, I'll bet it is, but in any case, someone installed the wrong ballasts in the fixtures and that is why they don't work well. I'm surprised they work at all. I hate 8 ft bulbs, they are so difficult to handle.

You have two choices, replace the ballasts with ones designed to run the bulbs you have, or scrap the whole thing, in which case I would save the ballasts, as they may prove to be useful on a 4ft T12 to T8 conversion or a replacement for a bad T8 ballast.

If you get new fixtures, get ones with standard T8 4 ft bulbs, they are easily found and cheap, in all variations of quality and color ranges.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
There are F96T8 Slimline w/ a single pin base, and F96T8HO lamps w/ a recessed double contact base. Slimline lamps **** in cold temps, the fixtures show single pin tombstone lampholders, but the ballast shown is for 2-32 watt T8 4' lamps.

OP's photo:

21086722.jpg


Edit: the ballast also will operate 2' & 3' lamps.
 
Last edited:
OP
M

Mr. Roboto

Well-known member
Joined
Dec 11, 2012
Messages
2,161
Location
New Hampshire
Thanks for all the feedback, however, I am still a little confused. I thought the T12 vs T8 bulbs described a difference in bulb diameter, not length. Are you all saying my bulbs must be T12 because an 8 foot T8 bulb does not exist?
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,770
Thanks for all the feedback, however, I am still a little confused. I thought the T12 vs T8 bulbs described a difference in bulb diameter, not length. Are you all saying my bulbs must be T12 because an 8 foot T8 bulb does not exist?

T8 lamps DO exist in 8 foot lengths, I did write F96T8 and F96T8/HO, which are 8' lamps, the HO ones do not apply to you though.
 
Last edited:

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Probably what happened originally was that your Father's place of work installed the wrong ballasts in the light fixtures and they did not work properly, so they finally removed them. Building maintenance gone astray.
 
OP
M

Mr. Roboto

Well-known member
Joined
Dec 11, 2012
Messages
2,161
Location
New Hampshire
Well, I will just have to look at the bulbs when I get home from work to see what they say on them. I will post back once I do.
 

eljefino

Well-known member
Joined
Feb 21, 2008
Messages
336
I wonder if you could yet save these by getting a mega-pack of two-pin tombstone lamp connectors and making each fixture take 4 foot T8s. Either rig them one long bulb then another (like walmart is doing now) or scrap half of them, steal their ballasts, and double up on the other fixtures.

This seems like rebuilding grandpa's ax with a new head and a new handle though. ;)
 

Kyle1500

New member
Joined
Dec 11, 2021
Messages
3
Post #1 is where were went astray.



The OP described them as 48 inch (4 ft) and no one apparently caught the fact they were single pin, which is not made in anything other than an 8 ft length. I'm not familiar with 8 ft T8 so I don't know if it is single pin or not, I'll bet it is, but in any case, someone installed the wrong ballasts in the fixtures and that is why they don't work well. I'm surprised they work at all. I hate 8 ft bulbs, they are so difficult to handle.

You have two choices, replace the ballasts with ones designed to run the bulbs you have, or scrap the whole thing, in which case I would save the ballasts, as they may prove to be useful on a 4ft T12 to T8 conversion or a replacement for a bad T8 ballast.

If you get new fixtures, get ones with standard T8 4 ft bulbs, they are easily found and cheap, in all variations of quality and color ranges.
Actually, there are single pin lamps available in 48 inches, but only as a T12. F48T12 would be a single pin lamp aka slimline, but is actually slightly shorter than the F40T12 we've come to know and love, because the sockets for slimline lamps take up more space than a normal bipin socket while the fixtures are the same length. F48T12 lamps are very uncommon and hard to find, but they do exist. Single pin T8 lamps are available in 72 and 96 inches.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,054
Location
Coronado, CA
i converted my 277 t-12's to 120, the ballasts were like 30 bucks a piece it wasnt too horrendous
I scored a bunch of magnetic ballasts when a previous employer changed from coil and core ballasts to energy efficient electronic ballasts.
The contractor who was hired by the utility was required to throw the removed magnetic ballasts into the dumpster, he very decently packed them all into a box that lay on top.
Recovery was very easy.
 

Racer_X

Well-known member
Joined
Jun 25, 2007
Messages
367
Location
MI
Actually, there are single pin lamps available in 48 inches, but only as a T12. F48T12 would be a single pin lamp aka slimline, but is actually slightly shorter than the F40T12 we've come to know and love, because the sockets for slimline lamps take up more space than a normal bipin socket while the fixtures are the same length. F48T12 lamps are very uncommon and hard to find, but they do exist. Single pin T8 lamps are available in 72 and 96 inches.