Flush Mounting Panel - Side Screws OK?

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
Just checkin...Probably the stupidest question asked here thus far :D
I've got a Square D Homeline Panel. Like every other panel I've seen, its got provisions for mounting in the back. Is it ok if I drill a 2-3 holes on each side so I can screw it right to the 2 studs?
 
To avoid these ads, REGISTER NOW!

nwav8tor

Well-known member
Joined
Feb 21, 2012
Messages
239
Location
Spokane, WA
Are you sure there aren't any knock-out slots on the sides for mounting to the studs? Mine has two on each side. Slots rather than holes to aid proper positioning to sit flush with the edge of the stud or drywall.

Paul
 
OP
S

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
Are you sure there aren't any knock-out slots on the sides for mounting to the studs? Mine has two on each side. Slots rather than holes to aid proper positioning to sit flush with the edge of the stud or drywall.

Paul

Hmm, I dont think so, but admittedly, I decided to open the box up and take a peek at the panel for the first time last night after I was done flashing the windows, it was quite dark. BUT from that initial look (and I did look for mounting holes on the sides) I didnt see anything...
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
With 1/2" drywall the holes are a 1/2" back on the stud and putting the screw on a slight angle you should be able to get a good bite into the stud.

Problem is they are too far forward on the studs. I had to drill new holes in the center
 

ForceFed70

Well-known member
Joined
Apr 27, 2010
Messages
3,441
Location
BC, Canada
If you flush-mount right to the studs, how do you get your wires into the panel? Are you planning to only enter the panel from above and below?

This is the reason you don't normally see a panel flush mounted directly to the studs.
 

MrMark

Well-known member
Joined
Jan 25, 2010
Messages
4,626
Location
Southern Cal.
With 1/2" drywall the holes are a 1/2" back on the stud and putting the screw on a slight angle you should be able to get a good bite into the stud.

I use 5/8 and don't like screwing things in at an angle. ;)I think it is bizarre that they put the holes (QO panel too) so close to the stud edge.
 
To avoid these ads, REGISTER NOW!

MrMark

Well-known member
Joined
Jan 25, 2010
Messages
4,626
Location
Southern Cal.
If you flush-mount right to the studs, how do you get your wires into the panel? Are you planning to only enter the panel from above and below?

This is the reason you don't normally see a panel flush mounted directly to the studs.

Yes, only above and below. This is the way it is done here for new construction.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
I do agree. You'd think they would have moved the holes back at least another 1/2" to 3/4".

I use 5/8 and don't like screwing things in at an angle. ;)I think it is bizarre that they put the holes (QO panel too) so close to the stud edge.
 
OP
S

Spudland_Dave

Well-known member
Joined
Mar 12, 2010
Messages
3,025
Location
Maine
-Wiring, yes all wires top and/or bottom. The house is wired like that even though the panel is surface mounted.

-I felt the same about the hole placement so I drilled a new set of holes further back.

Still didnt mount the panel, but I will soon.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
If you flush-mount right to the studs, how do you get your wires into the panel? Are you planning to only enter the panel from above and below?

This is the reason you don't normally see a panel flush mounted directly to the studs.
We see this ALL the US. It is SOP for flush mounted panels.
ALL new panels have mounting hole KO's on the sides.

I must say, Canadian codes are pretty normals with many in line with our NEC, but your sideways mounted panels are just plain WEIRD. ;)
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
Is different for us, but makes sense by putting all the breakers at an even height for ease of reach. I assume that's why the panel is placed sideways.

We see this ALL the US. It is SOP for flush mounted panels.
ALL new panels have mounting hole KO's on the sides.

I must say, Canadian codes are pretty normals with many in line with our NEC, but your sideways mounted panels are just plain WEIRD. ;)
 

rabidsquirrel

Well-known member
Joined
Jul 17, 2010
Messages
398
Location
SE Pennsylvania
Is different for us, but makes sense by putting all the breakers at an even height for ease of reach. I assume that's why the panel is placed sideways.

Ease of reach really isn't a good argument because of the size of homeowner panels. It's not like it's a 7' tall 3Φ 480V panel.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
Is different for us, but makes sense by putting all the breakers at an even height for ease of reach. I assume that's why the panel is placed sideways.


The reason Canukistani panel are mounted sideways besides the fact the CEC allows it, is that the main breaker are seperated from the distribution section & the load cables are not allowed to pass through it, so they find it easier to mount them sideways.

Art 240.81 is what prohibits this in the US.

240.81 Indicating. Circuit breakers shall clearly indicate
whether they are in the open “off” or closed “on” position.
Where circuit breaker handles are operated vertically
rather than rotationally or horizontally, the “up” position of
the handle shall be the “on” position.

Copied from the 2008 NEC.
 