I am looking into buying a commercial ice cream machine for home use. It is a 240V/60hz single phase machine where the owner or electrician would add the correct plug to it. Machine draw is 16 amps.
I see that locking L6-20P plugs are commonly deployed in commercial kitchens but is it really necessary at home? I see a few non locking 6-20P and 6-30P that would hug the wall outlet and not stick out like an "L" plug would. Since there's zero vibration going to the plug and there's zero chance of me snagging the cord that's behind the table, why go with a locking plug? Any advice and opinions would be great, thank you!
Also, is it OK to use an L6-30 outlet & plug on a 20-amp rated circuit breaker or should the breaker and wiring be upped to 30A?
I see that locking L6-20P plugs are commonly deployed in commercial kitchens but is it really necessary at home? I see a few non locking 6-20P and 6-30P that would hug the wall outlet and not stick out like an "L" plug would. Since there's zero vibration going to the plug and there's zero chance of me snagging the cord that's behind the table, why go with a locking plug? Any advice and opinions would be great, thank you!
Also, is it OK to use an L6-30 outlet & plug on a 20-amp rated circuit breaker or should the breaker and wiring be upped to 30A?