We moved some machines for a neighbor who recently built a garage. He had another neighbor help wire it. They did a beautiful job, very neat. They used an 8 space main breaker panel which was somewhat ok but it has all tandems already and I should have snapped a pic.
Picture perfect, 4 wire feed, no bond screw, but we have all the egc and the whites all on the same bar as well as the ground rods and the can is floating.
Super beautiful workmanship, one would never give it a thought that this isn't right. I knew a couple of these guys use to do handy work, when I see a friends install and it wasn't wired by a legit master I always check, sure as ****.
I am going to get a ground bar and take it down there ad go over it with the guy who dun it.
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,279
Location
Modesto, CA
Whoops!

Perhaps u should hand them a copy of the 4-wire feeder diagram for detached structures that we all post on here...