Its wild overkill for both, unless distance is massive, but it will workTwo projects come to mind right away:
1) Running power to the lower garage. Lights, fans, radio, power tools, and the blower on the wood stove.
2) Running power all the way across the house from the garage wall to the breaker box. Generator transfer switch lead. Would like the ability to run the well pump, heat, lights, refrigerator, and whatever else is needed - even if it requires two generators and a second run of cable. Topographical and geriatric challenges prevent having the generator on the same end of the house as the breaker box.
Conduit will be used in each case.
it clearly says THWN below THHN.It is THHN/ MTW rated according to what I'm seeing. I don't see the THWN wet rating. Most THHN is dual rated THWN, but I'm not seeing that here. When I have seen THHN/ MTW ratings, it has typically had more strands than "regular" thhn. But that is typically on smaller AWG sizes. The larger sizes may have the same strands.
looks like its only THHN/THWN, which means 90° dry/75° wet rating.Is it thhn or thhn-2? It will say on the jacket
If you only have 500 ft, I don't think I'd be buying more to complete these. You're head will explode when you get the priceThe run from the existing panel to a panel in the lower building would be somewhere approaching 300'.
The run from the existing panel to the end of the main garage would be somewhere around 110'.
It is THHN/ MTW rated according to what I'm seeing. I don't see the THWN wet rating.
I see it now....my apologies...it's "next to" the thhn rating. At least in one pic.... (seriously didn't see it previously)it clearly says THWN below THHN.
for 300+' youre looking at close to $1700 just to buy the other 3 conductors (in copper) you will need for a subpanel. It will be cheaper to buy a manufactured aluminum cable such as SER(above ground only) or MHF (conduit required indoors and above ground). 2/0 MHF will run you less than half that.The run from the existing panel to a panel in the lower building would be somewhere approaching 300'.
The run from the existing panel to the end of the main garage would be somewhere around 110'.
I'll get a photo of the jacket in a few minutes. Should clear that question up pretty definitively.



Where does the distance become massive?Its wild overkill for both, unless distance is massive, but it will work
So I'd need to run this stuff three times? Four?If you only have 500 ft, I don't think I'd be buying more to complete these. You're head will explode when you get the price
Saw this a bit late.for 300+' youre looking at close to $1700 just to buy the other 3 conductors (in copper) you will need for a subpanel. It will be cheaper to buy a manufactured aluminum cable such as SER(above ground only) or MHF (conduit required indoors and above ground). 2/0 MHF will run you less than half that.
do you have conduit between these panels? any underground portion between them?
I would try to sell the roll and use the proceeds to buy the cable you need. Home depot sells that roll for $1315 here. hell you could probably find someone to buy it for a $100 less than that and have plenty to buy the wire you need.
Its really a function of current draw plus distance. That wire could do a 100a subpanel up to 100-150ish ft, but not at 300ftWhere does the distance become massive?
What wire would be required for a 100A subpanel at 300'?Its really a function of current draw plus distance. That wire could do a 100a subpanel up to 100-150ish ft, but not at 300ft
totally dependent on the load and size of circuit youre runningPhotos of the cable jacket:
Where does the distance become massive?
yes if you want a 120/240v capable subpanel, you will need 3 conductors that are the same size and 1 conductor that is smaller for the EGCSo I'd need to run this stuff three times? Four?
The potential for savings to be had by already owning the wire is part of what perked me up. It would be great to be able to move forward with either of these projects ahead of schedule.
what size genny?Saw this a bit late.
Three other conductors. This might do the generator transfer switch circuit, then. Unless it's wildly inappropriate for the task.
you will need either conduit or a trench for direct buryThere is conduit through the house, but not below ground and through the yard to the lower building just yet.
depends on the sizeThere are several large rolls of aluminum cable here. Have not inventoried them just yet. If they would do either job really well without burning the place down, that could be interesting.
totally dependent on what equipment will be running concurrently and how many people will be working in there concurrentlyWhat wire would be required for a 100A subpanel at 300'?
Would a 100A feed be sufficient to run a full shop? Welder, compressor, lights, heater, radio, power tools, fans, and battery chargers? I don't weld, but may as well set the building up to be able to do whatever work happens to come down the line.
For a single person shop? 60a is usually plenty. Only time that tends to cause a potential problem is when you are plasma cutting while hvac is running. Your #2 copper would do about a 70a feed at 300ftWhat wire would be required for a 100A subpanel at 300'?
Would a 100A feed be sufficient to run a full shop? Welder, compressor, lights, heater, radio, power tools, fans, and battery chargers? I don't weld, but may as well set the building up to be able to do whatever work happens to come down the line.