furnace cycling

jkmech

New member
Joined
Jan 29, 2015
Messages
4
my furnace cycles on and off . it runs 10 minutes then shuts down for ten minutes and then starts again for 10 minutes contuinues the same way . any ideas?
 
To avoid these ads, REGISTER NOW!

mygarageone

Well-known member
Joined
Oct 16, 2013
Messages
2,691
Location
Munising , Mich
not near enough info to make an assessment.
Did this just start ? is this an older furnace ? what brand , hi eff or what ? have you changed the filter lately ?
Give us some details.
 

JRC3

Well-known member
Joined
Jun 30, 2014
Messages
12,481
Location
Southwestern OH
Does it have a flame rod/sensor? If so clean it. Remove it and clean it with a cloth or a dollar bill. It may look clean but it can be dirty, you wont see a bunch of buildup on it. They don't work like a thermocouple as they sense current (ground) through the flame itself and it doesn't take a lot to lose that continuity.


Could also be a blocked flue or cracked heat exchanger tripping the high limit switch.

This guy is awesome and his site links his Youtube vids. http://www.grayfurnaceman.com/ I've learned tons from him.
 
OP
J

jkmech

New member
Joined
Jan 29, 2015
Messages
4
furnace is a frigidare gas model g6ra it is about 5 yrs old. after problem started replaced thermostat no help. cleaned flame sensor and checked it is working normal. all limits switches are good does not trip high limit switch. furnace starts normal and runs for about 3 minutes then flame shuts off and furnace blower motor and induction motor stay on till furnace cools down. wait about 5 to 10 mins. and it does same thing again same way .keeps doing this till house gets up to temp selected.
 

JRC3

Well-known member
Joined
Jun 30, 2014
Messages
12,481
Location
Southwestern OH
Sounds like the board but who knows. I'd still check the flue for rollout and the exchanger for cracks.


Might be time to check water column line pressure or at least check btu flow timing at the meter for that appliance. If it's low, maybe the furnace's regulator's screen is clogged. Has there been main line service in your area?
 
To avoid these ads, REGISTER NOW!

zmaxmotorsports

Well-known member
Joined
Jan 11, 2013
Messages
11,948
Location
South of omaha
Sounds like the board but who knows. I'd still check the flue for rollout and the exchanger for cracks.


Might be time to check water column line pressure or at least check btu flow timing at the meter for that appliance. If it's low, maybe the furnace's regulator's screen is clogged. Has there been main line service in your area?

:wtf::headscrat
 

BillK

Well-known member
Joined
Aug 24, 2006
Messages
9,320
Location
Beautiful Southern Maryland
jk,
Just went through the same issue with my house furnace. Turned out to be a combination of a dirty pre-filter for the electronic air cleaner combined with a lot of buildup on the circulating fan. The combination caused the furnace to go into an over temp shutdown and it would do exactly what yours is. My go-to HVAC guy told me to take the filters out and see if it took care of the problem, which it did. After cleaning the filters it was a lot better but still did it once in a while. He told me to pull the blower and clean it real good. He was right, there was some buildup on the fan "blades" apparently just enough to cut down on airflow some.

Pull the filters and see if it acts ok. If so, you will know that you have an airflow issue.

Hope this helps,
 

bonneyman

Well-known member
Joined
Apr 22, 2010
Messages
8,788
Location
Desert SW
Newer furnaces and air conditioners are very airflow sensitive. This becomes more pronounced as higher and higher SEER rating equipment is installed on older homes.
Using the right filter and keeping it clean/replaced religiously is vital. Especially in heat mode. Low airflow while using the furnace can easily lead to an overheat condition. Not good!
But even if you're spot on with filter maintenance, you should still have your evap coils cleaned every 5-6 years. Because no filter catches 100% of the dirt.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,132
Location
SE MI
... does not trip high limit switch. furnace starts normal and runs for about 3 minutes then flame shuts off and furnace blower motor and induction motor stay on till furnace cools down. wait about 5 to 10 mins. and it does same thing again same way .keeps doing this till house gets up to temp selected.

jk,
Just went through the same issue with my house furnace. Turned out to be a combination of a dirty pre-filter for the electronic air cleaner combined with a lot of buildup on the circulating fan. The combination caused the furnace to go into an over temp shutdown ...

I'm with Bill. Sound like an over-temp shutdown.

I have a similar problem, but mine is a duct work design flaw (2 90° turns coming out of a horizontal furnace befor heating the main trunk line). Luckily t only happens ocassionally.
 

bazar01

Well-known member
Joined
Jan 30, 2009
Messages
326
Location
Leesburg, GA
I'm with Bill. Sound like an over-temp shutdown.

I have a similar problem, but mine is a duct work design flaw (2 90° turns coming out of a horizontal furnace befor heating the main trunk line). Luckily t only happens ocassionally.

+1.
If it's not a dirty A/C coil or low air flow due to dirty filter, the flame is too high. Can you throttle the gas **** a little?
 