So I went to turn on my AC tonight and knew right away something was wrong. I got a little air blowing from the vents for a min and then nothing. So I walked outside to make sure the fan and pump were running at the condenser. Both were on, so i walked into the basement.

I found the txv frosted up and the blower fan didn't sound like it was on. I pulled the cover just to see it come to a stop. There is a on off switch wired on the side on the furnace. I turned the furnace off and waited a few minutes. I flipped the switch back on and watched the blower fan come on full speed and within 2 minutes it got slower until stopping completely.

Is this the sign of a failing blower? Can I safely jumper out the control board and try to run the fan on the medium setting to see if its the board?

Any help would be appreciated.
 
To avoid these ads, REGISTER NOW!

Dave in VA

New member
Joined
Jan 24, 2010
Messages
3
Location
Virginia, USA
After the motor stops can you spin the blower wheel by hand? It should spin freely. If not, then it's probably time for a new motor.

You mentioned Downers Grove--We lived on Lemont Rd in the late 50's. The state took 1/2 of our front yard for the frontage road for the I-55 interchange. It looks alot different on Google Earth then when we lived there. Our old house is still there, but everything past it is entirely different.
 

oltruckag

Well-known member
Joined
Aug 10, 2007
Messages
171
Location
*******, GA
Is the blower motor hot to the touch after it runs for a min or two? Get a clamp-on amp meter and check the draw compared to the rating on the motor - I suspect you'll find the current draw is high.

It is possible the cap is bad (weak) but usually when they fail the motor won't run at all. After the motor stops on its own, give it a spin and see if it runs a bit longer. Could just be a $15 problem, not a $100 problem.
 
OP
T

tonydanzah

Well-known member
Joined
Nov 14, 2009
Messages
5,275
Location
the champagne of people
the housing to the motor is very hot. I have an amp clamp and can throw it on. What is the specs and can I hurt the motor if i bypass the capacitor?
 

Dave in VA

New member
Joined
Jan 24, 2010
Messages
3
Location
Virginia, USA
It won't run without the cap. There should be a tag on the motor or the furnace with the motor amp draw. If it's hot after just a few minutes, I suspect the motor bearings are shot.
 
To avoid these ads, REGISTER NOW!

danski0224

Well-known member
Joined
Jan 29, 2005
Messages
13,516
Location
Near Naperville, IL
the housing to the motor is very hot. I have an amp clamp and can throw it on. What is the specs and can I hurt the motor if i bypass the capacitor?

It's done.

Motor will not start w/o capacitor.

Motor specs are printed on a sticker that is usually covered by the motor mount bracket. Probably should be less than 10A- just a guess though.

You need a capcitior checker to test the cap.
 

bazar01

Well-known member
Joined
Jan 30, 2009
Messages
326
Location
Leesburg, GA
battery was dead in my amp clamp, but i did bypass the cap and the motor did the same thing. I think I have a meter with a cap setting somewhere
You seem comfortable with a meter so do the following.
Turn off the disconnect. Open the electrical cabinet access door. Look at the top of capacitor mounted on the blower housing, if it is bulging at the top, it is toast, you need a new start capacitor. Usually a 5mF capacitor. If the capacitor top is not bulging, you need a capacitance tester or get an analog meter set to resistance and watch the needle. If it pegs then drops, reverse the probes, if it pegs then drops, the capacitor is good. Then the motor is shot, Do a resistance test on the motor leads, common to start terminal and common to run terminals then report your ohm readings. Also do a ground test on the run and start terminals to ground and report back.
Good luck!
 
OP
T

tonydanzah

Well-known member
Joined
Nov 14, 2009
Messages
5,275
Location
the champagne of people
ok I found out my fluke 289 does have a cap testor setting along with the diode testor. There is no change on the meter when i touch the leads or switch directions. I also have a simpson 260 that I bought to check a piece of forklift potentiometer. Not to familiar with it. But set on 1ohm, 100ohm or 10k ohm the needles do not move in either direction.
 

bazar01

Well-known member
Joined
Jan 30, 2009
Messages
326
Location
Leesburg, GA
ok I found out my fluke 289 does have a cap testor setting along with the diode testor. There is no change on the meter when i touch the leads or switch directions. I also have a simpson 260 that I bought to check a piece of forklift potentiometer. Not to familiar with it. But set on 1ohm, 100ohm or 10k ohm the needles do not move in either direction.

Not familiar with Simpson 260, is it an analog meter? If it is, the test should work.
I forgot to mention, did you pull the wires off the cap when you tested for resistance? If not, pull the wire leads off the cap and retest.
 
OP
T

tonydanzah

Well-known member
Joined
Nov 14, 2009
Messages
5,275
Location
the champagne of people
Not familiar with Simpson 260, is it an analog meter? If it is, the test should work.
I forgot to mention, did you pull the wires off the cap when you tested for resistance? If not, pull the wire leads off the cap and retest.

simpson 260 is analog. I pulled the cap for the furnace to bring upstairs to test it. The meter works, as the needles moves is i touch the probes together.
http://www.drillspot.com/products/118847/Simpson_260-8_Analog_Multimeter?s=1

same meter but i bought mine dirt cheap on ebay

but just like on the fluke 289 cap testor i get no change.
 

bazar01

Well-known member
Joined
Jan 30, 2009
Messages
326
Location
Leesburg, GA
simpson 260 is analog. I pulled the cap for the furnace to bring upstairs to test it. The meter works, as the needles moves is i touch the probes together.
http://www.drillspot.com/products/118847/Simpson_260-8_Analog_Multimeter?s=1

same meter but i bought mine dirt cheap on ebay

but just like on the fluke 289 cap testor i get no change.

Ahh, ok, it is analog, perfect.
The cap is dead, and since you mentioned the motor was hot, it was trying to start but the cap is dead so it does not spin.
Just to make sure, do a resistance test on the motor start and run windings to common just to make sure the motor is good. Then write down the ohm readings for each.
Then put the probe on the start and run terminals and you should get a resistance equal to the sum of each if the motor is good.
 
OP
T

tonydanzah

Well-known member
Joined
Nov 14, 2009
Messages
5,275
Location
the champagne of people
alright the neighbor had an hvac buddy that let me buy the cap off his van. I put it in and the motor fired right up. Who knows how long the 22yr old motor will last after running with a blown capacitor.
 

oltruckag

Well-known member
Joined
Aug 10, 2007
Messages
171
Location
*******, GA
alright the neighbor had an hvac buddy that let me buy the cap off his van. I put it in and the motor fired right up. Who knows how long the 22yr old motor will last after running with a blown capacitor.

I change caps in condensing units all the time that have been running (well, humming and tripping on internal overload ;)) with bad caps. I'm sure it shortens the lifespan of the motor, but they usually fire right up and run fine for years.

Glad it was a cheap/simple fix.
 