Furnace guys...why is this dripping?

bassbone52

Well-known member
Joined
Jan 7, 2011
Messages
516
Location
Central Indiana
25 year old Lennox Pulse furnace. Recently water has started to drop from the bottom of this 2- inch PVC pipe where the black cap is held by a spring clamp. Seems like it started after I broke the 1/2" PVC tube coming out of the side of the two-inch PVC. Is this a drip leg that normally fills up then empties thru the half-inch to the floor drain? How do I fix this?
 

Attachments

  • image.jpg
    image.jpg
    14.2 KB · Views: 134
To avoid these ads, REGISTER NOW!

dw1

Well-known member
Joined
Jan 26, 2015
Messages
1,335
Location
Ky
thats your condensation trap, take the spring clamp and black rubber piece off and drain the water out of it, its probably full (use a bucket or something to catch the water)

It will eventually drain out your broken 1/2" pvc piece. I just replaced the exact same furnace last year.
 
Last edited:
To avoid these ads, REGISTER NOW!

danielzig

Well-known member
Joined
Dec 14, 2008
Messages
175
Location
Chicago, IL
That is correct. The water fills the 2 inch leg and then goes out the half inch line. An annual maintenance item should be removing the black cap and draining any debris out.

I also just replaced my pulse last year. Great furnace, noisy as heck. Be sure to have it pressure tested every year.
 

Jackfre

Well-known member
Joined
Dec 26, 2010
Messages
4,411
Location
N CA
The Pulse had a recall some years back. They used the wrong weld process to join the two HX's and they were cracking. If it hasn't been checked against the recalled units I would suggest doing so. And, for safety and common sense purposes get CO detectors.
 