We have a rheem furnace with a Econet smart thermostat. Currently thermostat is set to 67* and it is showing house is currently *69. Why would the furnace turn on and run. I just started noticing it doing this.
 
To avoid these ads, REGISTER NOW!

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,967
Location
Peace Valley,mo
Gas furnace? Model number of stat?
Older bimetel thermostats had a heat anticipator that was set by either amps by gas valve or burner control. This would shut the gas valve off and blower would run to get all the heat out of the heat exchanger. Rhen the blower would shut down and room temp would be at setpoint. Page 31 anticipator if this is your stat. Under setup. When making a change take baby steps. If it set at 0° try -1° let it run few hours before making another change.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,420
Location
VT
is it blowing heat? or just running the fan to circulate the air in the house?

This was my first thought.

My second thought was I'm pretty sure mine starts the fan again a few minutes after the initial burn is done, to get the residual heat out.
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,967
Location
Peace Valley,mo
This was my first thought.

My second thought was I'm pretty sure mine starts the fan again a few minutes after the initial burn is done, to get the residual heat out.
If the fan restarts after the burners are off the fan hasn't run long enought the first time. If the fan control is in a box 21/4" x 3" and a round dial inside "do not turn dial" hold dial there are three settings right one move cw just a little 1/16" try that have to give furnace 5 minutes to see if it comes back onafter it shut downs. That dial is mounted to a bimetel spring. Come back on move it another 1/16".
 

bonneyman

Well-known member
Joined
Apr 22, 2010
Messages
8,773
Location
Desert SW
If the fan restarts after the burners are off the fan hasn't run long enought the first time. If the fan control is in a box 21/4" x 3" and a round dial inside "do not turn dial" hold dial there are three settings right one move cw just a little 1/16" try that have to give furnace 5 minutes to see if it comes back onafter it shut downs. That dial is mounted to a bimetel spring. Come back on move it another 1/16".
Sounds like the old Honeywell bimetal coil fan/limit switch.

Like this one?
 
To avoid these ads, REGISTER NOW!

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,967
Location
Peace Valley,mo

htmdude57

Well-known member
Joined
Apr 28, 2014
Messages
173
Location
Hudson Valley, New York
I agree with fitter30. There are 2 problems. The temperature of the house is overshooting. And the fan kicks on a second time. As he said, go into the thermostat to the anticipator setting and lower the number. That should cut down on the temperature overshoot. But for the extra fan kicking on, the setting I believe you need to adjust is the pointer on the left. See the diagram. Its marked #1 in this diagram. Move the pointer a little to the left, so the fan will run till the internal temp of the furnace is around 75 degrees. Then the furnace shouldn't kick on for the extra run.
 

Attachments

  • fan control.png
    fan control.png
    375.4 KB · Views: 6
  • anticipator.png
    anticipator.png
    211.8 KB · Views: 6
OP
R

Reit38

Well-known member
Joined
Nov 12, 2011
Messages
626
Location
Iowa
The fireplace will shut off like normal. But inwill notice it running again latter when the temp is above the set temp. We have a wood burning fireplace going most of the time
 
OP
R

Reit38

Well-known member
Joined
Nov 12, 2011
Messages
626
Location
Iowa
Tonight I noticed again that the thermostat was reading tempnwas 71 when set temp is set to 69 and the furnace was running
 

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,967
Location
Peace Valley,mo
Having a fireplace running with a furnace. Fireplace is adding heat to the house getting picked up from the return air one possibility. Thermostat is showing 71 set at 69 when does it come back on? Made any adjustments like post 3.
 