Furnace Problem Help!

Gooch

Well-known member
Joined
May 30, 2009
Messages
676
Location
Petersberg, IA
Sorry, not garage related.

I had a new Tempstar furnace installed about 2 years ago. just the last week or so it started cycling quite frequently. the Tstat is set to 60 overnight and in the morning when it brings it back up to 67 it will run for two or three minutes then shut off for a minute then run for two or three minutes, then shut off. it will repeat this until it eventually gets the house back up to temp.

Any insight?
 
To avoid these ads, REGISTER NOW!

HoosierBuddy

Well-known member
Joined
May 9, 2006
Messages
2,915
Location
Southern Indiana
I'd suggest you need to have a qualified service person come out and fix it for you. It'll waste a lot of energy short cycling like that.

Phil
 
To avoid these ads, REGISTER NOW!

Dkramer

Well-known member
Joined
Dec 30, 2009
Messages
50
Location
Grants Pass, OR
Have you changed the filter lately?



What fault code is the cnt. board giving?

I agree, check your filters and check for a fault code. Most modern furnaces will go into a lockout if the furnace limits several times (3 or so)during a run cycle. Doesn't sound like it has done that, so your filters are probably OK. If filters are clean and no fault code is visible, call the installing company for service.
 

Cuda

Well-known member
Joined
Apr 13, 2010
Messages
244
Location
Utah
Also make sure your return air ducts are not blocked by anything. It sure sounds like a lack of air movement is causing the safety switch to open.
 