wrench409
Well-known member
My Furnace - Frigidaire FG6RA - installed in 2008 has begun to cycle out after a complete startup. It's an 80% type.
First, it has LEDs to flash fault codes - RED on for Power and is used to flash codes when codes are present - YELLOW on for the flame sensor and it flashes when it is out of range. However, no codes are displayed.
1. Set tstat to temp above ambient - call for heat.
2. Inducer motor spins up.
3. Igniter glows normally.
4. Gas valve cycles on.
5. Burners ignite.
6. Yellow LED comes on signalling the flame sensor is providing signal.
7. After burning for a very short time - 45 seconds, the fan blower motor powers up.
8. After 60 seconds the Yellow LED goes out, the system shuts off and this cycle repeats.
Things I've checked or done so far:
a. New filter - get's one every 4~6 weeks anyway
b. Removed the flame sensor - not very much build up, but I cleaned it anyway. This is the most common on these NG furnaces and it was worth a shot.
c. Checked the pressure switch port to the plenum for buildup, found none.
d. Checked for wiring connection issues in the unit - found none.
e. Cussed a lot.
I am experienced in troubleshooting flash codes to check sensors and circuitry since the 80's. I am trained in electrical and electronics. I already do my own home A/C service (same unit).
This damn thing has me pulling my hair out. All the vids on the net say clean the flame sensor and you're done. It's indicative the flame sensor has failed but not knowing the sensor specs, I'm not sure.
No codes to troubleshoot. No sensor data to check input/output on my meter. HVAC techs want $28 on the net to answer and local HVAC guys won't answer anything.
I hate throwing parts at anything until it's fixed. And the local supply house wants $58 plus S&H for a $10 sensor.
Any other stuff I need to look at?
I'm stumped.
First, it has LEDs to flash fault codes - RED on for Power and is used to flash codes when codes are present - YELLOW on for the flame sensor and it flashes when it is out of range. However, no codes are displayed.
1. Set tstat to temp above ambient - call for heat.
2. Inducer motor spins up.
3. Igniter glows normally.
4. Gas valve cycles on.
5. Burners ignite.
6. Yellow LED comes on signalling the flame sensor is providing signal.
7. After burning for a very short time - 45 seconds, the fan blower motor powers up.
8. After 60 seconds the Yellow LED goes out, the system shuts off and this cycle repeats.
Things I've checked or done so far:
a. New filter - get's one every 4~6 weeks anyway
b. Removed the flame sensor - not very much build up, but I cleaned it anyway. This is the most common on these NG furnaces and it was worth a shot.
c. Checked the pressure switch port to the plenum for buildup, found none.
d. Checked for wiring connection issues in the unit - found none.
e. Cussed a lot.
I am experienced in troubleshooting flash codes to check sensors and circuitry since the 80's. I am trained in electrical and electronics. I already do my own home A/C service (same unit).
This damn thing has me pulling my hair out. All the vids on the net say clean the flame sensor and you're done. It's indicative the flame sensor has failed but not knowing the sensor specs, I'm not sure.
No codes to troubleshoot. No sensor data to check input/output on my meter. HVAC techs want $28 on the net to answer and local HVAC guys won't answer anything.
I hate throwing parts at anything until it's fixed. And the local supply house wants $58 plus S&H for a $10 sensor.
Any other stuff I need to look at?
I'm stumped.
I would also jump out R and W at the unit, eliminate the t-stat. If that doesn't work I would get a magnehelic gauge or manometer on the inducer port and verify that it is producing what is needed to make the pressure switch. If there is build up in the chimney or vent pipe or bad inducer motor/capacitor you could be having a prob that way.