I am in the process of finishing a complete renovation of the second floor of my house. It was previously an up/down split duplex, and will now be one home.

The existing furnace was a 70,000 BTU, 80% efficiency which heated the upstairs satisfactorily. At that time, the walls were uninsulated, the windows were 50/50 new vinyl and original single pane, and the ceiling was very poorly insulated.

The upstairs is now 2x6 walls with R19, brand new low-E aluminum-clad wood windows, and R-19 base in the attic which will be blown to R-60 when the duct work is installed.

I am going with a new 2-stage, 95% efficient furnace. It seems to be that a 46,000/32,000 BTU will be plenty sufficient, especially since being opened to the downstairs, heat will come from the downstairs furnace system. However I am concerned and don't want to undersize. Air will be fed from the ceiling.

Does 46/32k BTU 2-stage sound like it will be plenty?
 
To avoid these ads, REGISTER NOW!
OP
I

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
Also, house is double layer brick with a 2" air gap between the bricks, floor between upstairs/downstairs is insulated with R19 primarily for sound deadening though I doubt that matters.

I am wondering if I will also want a way to exchange air upstairs with the air downstairs, and vice versa? Each floor has its own HVAC system.
 
To avoid these ads, REGISTER NOW!

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,372
Location
Michigan
70000X.80=56000
46000X.95=43700

The only way to know for sure is to do a heat load calc, aka a Manual J

With the added insulation and new windows I would be surprised if you needed more then the 46k.
 