Furnace won't run properly...

AeroMoto

Member
Joined
Jan 10, 2014
Messages
15
Location
Indianapolis
Lennox Conservator III G16 Upflow model
Robert Shaw Controller SP735L
Robert Shaw Grayson 7100 DER-S7C regulator
I believe the fan and limit controller is a Honeywell of some kind.

The inducer motor turns on and runs just fine. I can hear the ignitor click on. A few seconds later the burners kick on and then shut off after a few seconds. It seems to me that the flame sensor (or thermocouple?) is not functioning properly. The main blower never kicks on I'm assuming because the flame sensor is malfunctioning and not detecting a flame. So how do I troubleshoot it? I'm not quite sure where it's located, but any help is appreciated. It's cold in the house!
 
To avoid these ads, REGISTER NOW!

domain

Well-known member
Joined
May 16, 2010
Messages
902
Usually near the last of the burner tunes. This insures that they all light.
 
OP
A

AeroMoto

Member
Joined
Jan 10, 2014
Messages
15
Location
Indianapolis
I cleaned the flame sensor and ignitor with the scotch brite pad, and the same results. The flame sensor had cracked ceramic insulation and I could move the metal probe up and down about 1/8". So I'm thinking the sensor is cracked and bad.
 
To avoid these ads, REGISTER NOW!

TOOL FANATIK

Well-known member
Joined
Sep 20, 2014
Messages
566
Location
Bennington, VT
the problem does sound like the flame detector is not detecting a flame; we can all agree on that. now what is the root cause? it could be the actual flame detector is bad. im assuming this is a gas furnace?
 