Okay- total newb deal here.
I have a garage built in the stone age-just kidding- but close.
I have a single slot, fuse box.
I want to change this out to a breaker panel for obvious reasons.
I have access to turn off the feed, can take care of that.
Is this really as plug and play as it appears, disconnecting the hot wires where they come in and reconnecting or?
 
To avoid these ads, REGISTER NOW!

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,577
Location
East Bay SFO
What is the gauge of the wire feeding your current single fuse? That might severely limit your options. I hope you’re not planning to hook a 12 ga. ungrounded cable to a big sub panel.
What electrical loads are you anticipating in that garage? Plan ahead.
You might consider running a new feed from your main panel and do it properly.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,067
Location
Modesto, CA
No not plug N play.

Is the current circuit grounded with an EGC?

You will need to add ground rods.

I second what shiftless said.

What is the gauge of the wire feeding your current single fuse? That might severely limit your options. I hope you’re not planning to hook a 12 ga. ungrounded cable to a big sub panel.
What electrical loads are you anticipating in that garage? Plan ahead.
You might consider running a new feed from your main panel and do it properly.

:+1:
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,771
Location
NW Iowa
^ This, if only has a #14 or 12 wire feeding it just leave the fuse box alone until you decide to upgrade the rest.

What are your obvious reasons? Do you blow fuses often? That's not the fuses fault, it means you have inadequate wiring.
 
To avoid these ads, REGISTER NOW!
OP
F

FarmerWill

Well-known member
Joined
Dec 6, 2017
Messages
293
Location
South Texas
Have an electrician coming out to do this for me.
Haven't blown a fuse in forever- but.
All the fuse box is running is one freezer, three lights and a single quad box.
This is the start of a major overhaul of the building.
I have never plugged in anything bigger than a drill or a jig saw.
Like to be able to run a small compressor, my little mig welder and such in this building.
Let you know how it goes.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,771
Location
NW Iowa
So you need to upgrade the whole feeder to the building not just the fuse box.

A correctly sized fuse is actually better than a breaker in some ways. A fuse will never fail to blow if you overload the circuit where old breakers sometimes do not trip. There are also many classes of fuses commonly available to better protect motors/ect, unlike residential breakers. The fuse is less convenient if you do blow it and you have the problem of everybody putting 30A fuses in 15 and 20 amp circuits.
 