If the fixtures are 1.5 years old they are likely the pulse start variety, which usually means that they contain in addition to the ballast transformer a capacitor and ignitor. The ignitor is usually the first thing to give up. Worn, defective or old lamps contribute to the stress on the ignitors, when the lamps characteristics change due to age. It takes longer for them to start, sometimes multiple re-strikes, before they finally reach operating temperature.
You didn't state what the wattage is only that they are metal halide. 19 fixtures would suggest a large lot, and large fixtures to go with it. 400WMH would be my guess.
Looking up a couple of different manufacture's cut sheets for 400WMH pulse start ballasts. Venture lighting calls for a 6A fuse, Advance calls for a 7A fuse both @ 208V. This may be part of the problem if indeed they are 400W units.
Another thing to check if you have to get a lift is, are the lamps the correct type to match the ballast? There is a ANSI code type on the ballast, M59 for one example, and the lamp type needs to match, for the fixture to operate correctly. Many times I have come across fixtures with the wrong lamp type but correct wattage installed, causing early failure, ballast or lamp.
Check the startup of the remaining fixtures from a cold start at night. Do any do a re-stike before reaching temperature, or glow dimly not getting to full temp? Take an amp reading if you can of the operating units while starting and running. Poor starting performance is usually related to a degraded lamp, stressing the ignitor.
If you find poor starting of several, it would suggest you need a group lamp replacement to prevent future problems. It's cheaper to do it, one time, while the lift is there.
I find that there can be a great disparity in longevity of lamp life from different lamp manufacturers, in my own fixtures. Some last 1.5 years and others 5 years in the 175WMH pole fixtures I run. On a similar operating schedule as you mentioned earlier.
The installer of the fuses did you a good favor by installing them in the base, where ground accessible. Prevents loosing the other fixtures on the string with a short, and keeps the loop on for testing while you service the bad fixtures.