So I just got my 24000btu pioneer 220 volt system. I see it says min wire amps is 15 and max breaker size is 25 amps. So min wire size is a #14 but obviously if I put a 25 amp breaker on that the wire would go up. I already have a 20 amp 220v circuit I ran years ago for woodworking. Yes it’s 20 amp 220 and #12 wire.

Does the unit pull 25 amps or would I be good reusing the 20amp 220v feed I already have in the panel
 
To avoid these ads, REGISTER NOW!

brewchief

Well-known member
Joined
Sep 20, 2008
Messages
2,370
Location
Michigan
You can safely and legally wire it with #14 wire and a 25 amp breaker, there is an exception in the code that allows it.

Sent from my XT1254 using Tapatalk
 

Milton Shaw

Well-known member
Joined
Feb 11, 2011
Messages
4,835
Try what you have and if it blows breaker, get the 25 amp. But it will probably work OK the way it is...
 
To avoid these ads, REGISTER NOW!

TRWham

Well-known member
Joined
Aug 11, 2017
Messages
1,955
Location
East Cobb County, Georgia
I wasn't aware of that. Do you know the logic behind the exception?

Electric motors can draw very large current briefly when starting, and HVAC units have the largest motors you'll see in most homes (big *** air compressors being an exception). These units will be internally protected against sustained overload, so the NEC allows larger breakers on the branch circuits that power them to allow the starting current to pass without nuisance trips, while that internal protection prevents overload that might damage the conductors. Article 440 in the NEC covers wiring requirements for HVAC units.
 