It sounds like a lot of wires. You will need to calculate the fill of the conduit to make sure you are legal. In additon, if you exceed three conductor (not counting grounds) wires in a conduit, you will need to start looking at derating of the circuits, after 9 wires, the derating becomes serious enough to warrant lower amperage breakers, or more conduit runs to get out of the situation.
Even with deep 4" boxes, the box fill will need to be calculated also. If a wire comes into the box, connects at a wirenut and then the wire continues out, it is two wires for the count, if the wire passes thru the box without interruption, it is one wire. Again, you will have to sit down and calculate square inches of area of the wires based on NEC tables and fill based on cubic size of the box and the cu size of the cover (they should be marked) and you have to count devices in the box also (receptacles) and each device equals a certain number of the largest size of wire in the box (its two wires equivalent I think, its late and I don't feel like looking it up right now).
If you run all of this stuff together, you can share the green ground, but it has to be properly sized for the largest circuit.
You CANNOT use a white wire for a earth ground, it must be green or green/yellow striped only, or a bare wire. You CANNOT remark the ends of the wire used in conduit for any reason, until you get up to 1/0 (I forget the exact size cutoff, where, above that size you can remark a black wire as a neutral. In any case, it is well above any sizes you are installing).
Trying to put everything in one conduit is a BAD plan. You have to pull all the wires at one time, or you get a tangled mess.
Charles