Garage ceiling/bedroom floor insulation?

StickyRust

Member
Joined
Sep 18, 2020
Messages
5
Location
PA
I have an attached, unheated, 2 car garage with 2x8 joists. Above the garage are 3 bedrooms and 2 bathrooms. I just finished removing ~R13 fiberglass and OSB from the garage ceiling.

I have decided to reinsulate with Rockwool.

Option #1:
i04jEnh.png


1.5" EPS(that I have extra of) right up against the subfloor, caulked, then R23 5.5" Rockwool

R28.75 total insulation

Option #2:
Just install R30 7.25" Rockwool

-----

I really do not want to use drywall, can I perhaps just use plywood because i am using Rockwool?

Thanks!
 
To avoid these ads, REGISTER NOW!

e36jon

Well-known member
Joined
May 2, 2013
Messages
237
Location
San Francisco CA
Out here code for garage ceilings with occupancy above is two layers of 5/8 drywall, plus a bunch of detail stuff around penetrations and such, all in the name of fire safety.

I am also using rock-wool in my similar situation for both added fire safety and better sound suppression that fiberglass. That said, by the time rock-wool is showing off it's superior fire resistance I would say the game is already lost...
 
OP
S

StickyRust

Member
Joined
Sep 18, 2020
Messages
5
Location
PA
Out here code for garage ceilings with occupancy above is two layers of 5/8 drywall, plus a bunch of detail stuff around penetrations and such, all in the name of fire safety.

I am also using rock-wool in my similar situation for both added fire safety and better sound suppression that fiberglass. That said, by the time rock-wool is showing off it's superior fire resistance I would say the game is already lost...

yeah, so the drywall is just if I want to comply with code that hasn't been in compliance for 40 some years :bounce:

so my only question is the foam + rockwool or just rockwool
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,809
Location
VT
Foam, if edge sealed with canned foam, can air seal and reduce fumes and air exchange.

But don't be a cheapskate, whatever you do use 5/8 rock to bring it to code.
 
OP
S

StickyRust

Member
Joined
Sep 18, 2020
Messages
5
Location
PA
Foam, if edge sealed with canned foam, can air seal and reduce fumes and air exchange.

But don't be a cheapskate, whatever you do use 5/8 rock to bring it to code.

i.imgur.***/i04jEnh.png

It wont let me link, but replace the .*** with .com to see what I was going for

the plywood I want to use will actually be more expensive than sheetrock, i just have no desire to deal with sheetrock
 
To avoid these ads, REGISTER NOW!

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
22,809
Location
VT
i.imgur.***/i04jEnh.png

It wont let me link, but replace the .*** with .com to see what I was going for

the plywood I want to use will actually be more expensive than sheetrock, i just have no desire to deal with sheetrock

Yes, if you foam seal the rigid foam and then use glass or roxull you get better performance.

The 5/8 sheetrock is about fire code and life safety. Do it right.
 

Kaizen

Well-known member
Joined
Jan 9, 2015
Messages
6,948
Location
New England
Using roxul should be good with air sealing. If you have water pipes up there I’d insulate all of those with rubber insulation as well.


Sent from my iPhone using Tapatalk
 

pvanderlugt

Well-known member
Joined
Nov 14, 2010
Messages
335
^^^^^... This is good info from the fire chief.... I would take his advice... like the commercial says, he has probably seen a thing or 2...
 