My garage currently only has 120 available. I am in the process of rewiring a saw motor and a compressor motor to 240v.
The saw will draw 6.5 amps and the compressor motor will draw 11 amps.
I have 6R-15 plugs on both of them.
The total length of wire in the new circuit is about 30 feet.
I would normally use 12 gauge wire and a 20 amp breaker, but since there is a chance I might upgrade to a higher amp compressor motor, is it okay if I go ahead and use 10 gauge wire and a 30 amp breaker? Or should I run the 10 gauge wire and use a 20 amp breaker?
My receptacles are going to be 6-20r.
Any advice is greatly appreciated.
Cheers