I've tried several times to make this short and readable, but can't make it short, maybe I haven't made it readable
I understand the concept of using the EMT conduit as a ground, but I have chosen to run separate grounds with each circuit.
I want to place 4 enclosure boxes around my garage connected with EMT conduit. The "worst" of my conduits will contain 4 separate circuits: 3 for ceiling lighting, and the 4th for my 2 future garage door openers.
Reading other poster's questions, and trying to decipher the NEC code this is what I understand.
Derating with more than 3 current carrying conductors for me will be 70% so 70% of a rated 30 amp wire is 21 amps so I am ok there.
Max physical number of conductors in a 1" EMT conduit is 26.
Max fill however is 40%. So a 1" conduit should have no more then 10.4 wires?
My 4 above circuits have a total of 12 conductors, but only 8 count as current carrying.
Still my fill rate will be 46% so I l'll need to up to 1 1/4" conduit?
Thanks for any help.
I understand the concept of using the EMT conduit as a ground, but I have chosen to run separate grounds with each circuit.
I want to place 4 enclosure boxes around my garage connected with EMT conduit. The "worst" of my conduits will contain 4 separate circuits: 3 for ceiling lighting, and the 4th for my 2 future garage door openers.
Reading other poster's questions, and trying to decipher the NEC code this is what I understand.
Derating with more than 3 current carrying conductors for me will be 70% so 70% of a rated 30 amp wire is 21 amps so I am ok there.
Max physical number of conductors in a 1" EMT conduit is 26.
Max fill however is 40%. So a 1" conduit should have no more then 10.4 wires?
My 4 above circuits have a total of 12 conductors, but only 8 count as current carrying.
Still my fill rate will be 46% so I l'll need to up to 1 1/4" conduit?
Thanks for any help.