Garage door opener outlet

mrhul

Member
Joined
May 5, 2018
Messages
10
Hi guys,

My garage outlet has connected to only one outlet currently and I wonder if I can convert this into two outlets. Heres pics.thank you!
brHQFq3

phBmB3V
 
To avoid these ads, REGISTER NOW!

Shiftless

Well-known member
Joined
Mar 9, 2014
Messages
14,601
Location
East Bay SFO
Sounds like you might be inexperienced doing that sort of thing. Be careful. Do you have any nearby friends more familiar with electrical?

With that being said, Yes, but realize that if you change the receptacle, code requires GFCI protection. That receptacle is probably not on a separate circuit, so you might want to change the first receptacle on the string to GFCI even if you’re not expecting an inspector. My brother was almost killed because his garage circuit was not GFCI protected.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,089
Location
Modesto, CA
I see no pictures or icons for a picture.

But why does an outlet in the ceiling for the garage door opener require GFCI protection? It's unlikely to get wet I cannot reach it at 10 ft overhead without a ladder.

All garage outlets are required to be GFCI peotected now. Location doesnt matter
 

yatg

Well-known member
Joined
Aug 16, 2019
Messages
2,836
Location
Southern Oregon
But why does an outlet in the ceiling for the garage door opener require GFCI protection? It's unlikely to get wet I cannot reach it at 10 ft overhead without a ladder.

Exactly, you can plug in an extension cord.

Or the unlikely event that something major goes wrong with the opener and a metal garage door is electrified.

The safety monitors create rules to protect against worst case scenarios, even if it doesn't apply to you.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
The GFCI for the opener cant be up on the ceiling. It has be readily accessible to reset it, not using a ladder. That doesn't mean using a extension cord either. The receptacle has to be up there, Just not the GFCI. Either a dead front GFCI on the wall or protected by a GFCI circuit.
 

Git

Well-known member
Joined
May 18, 2008
Messages
6,894
Location
S Cal
Here are his pics (the easiest way to see what is going on when they don't show up is to click on the quote button to see what the poster typed)

I have never heard of ibb.co
https://ibb.co/brHQFq3
https://ibb.co/phBmB3V
 

Attachments

  • 60-F2-B5-C5-D16-E-45-C2-9-F0-A-33-E327-E32-EE6.jpg
    60-F2-B5-C5-D16-E-45-C2-9-F0-A-33-E327-E32-EE6.jpg
    63.3 KB · Views: 106
  • 87-A257-E3-3-EE5-47-EA-8-ABB-83413-B43-CBC7.jpg
    87-A257-E3-3-EE5-47-EA-8-ABB-83413-B43-CBC7.jpg
    49.6 KB · Views: 89

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
25,999
Location
Niagara Region, Ontario, Canada
All garage outlets are required to be GFCI peotected now. Location doesnt matter

He hasn't mentioned where he lives, if he's in another country besides the US the regulations may be different.

correct, here if the garage is detached different rules apply from attached. my detached did not need at arc fault or GFCI , except near sink .
 
OP
M

mrhul

Member
Joined
May 5, 2018
Messages
10
Sorry for the delay message. I have attached garage and I live in NJ.

I am pretty sure this is a separate circuit. If extension cord is an option, which one should I buy?

If not, then I was thinking to extend from outlet next to it using conduit and use GFCI? Here's another picture.

unnamed1.jpg
 
Last edited:
OP
M

mrhul

Member
Joined
May 5, 2018
Messages
10
By the whole point to get the plug is to able to install this garage door opener.

meross Smart Wi-Fi Garage Door Opener Remote
 

Git

Well-known member
Joined
May 18, 2008
Messages
6,894
Location
S Cal
Ok, it looks like you want to install some sort of smart/wifi remote for your garage door?

attachment.php


Sometimes people on Garage Journal can get carried away with the things... If I was in your shoes, I would just change out the current receptacle and add a standard duplex, or even easier would be to just add an adapter like this.

attachment.php
 

Attachments

  • TRI -051.jpg
    TRI -051.jpg
    138.7 KB · Views: 363
  • TRI -052.jpg
    TRI -052.jpg
    82.5 KB · Views: 362
To avoid these ads, REGISTER NOW!
OP
M

mrhul

Member
Joined
May 5, 2018
Messages
10
Ok, it looks like you want to install some sort of smart/wifi remote for your garage door?



Sometimes people on Garage Journal can get carried away with the things... If I was in your shoes, I would just change out the current receptacle and add a standard duplex, or even easier would be to just add an adapter like this.

Thanks Git. Can you please tell me what do you mean by change current receptacle and standard duplex? How to choose receptacle? And is it allowed to change? little confusion here.

I am leaning toward the second option to add an adapter but I am not sure which one would be a safe choice.
 
Last edited:

acer66

Well-known member
Joined
Dec 4, 2010
Messages
4,418
Location
Western North Carolina
Thanks Git. Can you please tell me what do you mean by change current receptacle and standard duplex? How do I tell if it is 15 amps or 20 amps? And is it allowed to change?

I am leaning toward the second option to add an adapter but I am not sure which one would be a safe choice.

You have a single and a duplex receptacle gives you two in the same format without having to tear out drywall.
Looks like the ones you most likely have throughout your house.

Find the breaker that feeds the receptacle but but even if that is a 20a circuit you can use a 15a duplex receptacle.
 
OP
M

mrhul

Member
Joined
May 5, 2018
Messages
10
It looks like I have 15 amp circuit. I just tested it. Can't tell if it is GFCI or not. To me it looks it is not.

unnamedG.jpg
 

Git

Well-known member
Joined
May 18, 2008
Messages
6,894
Location
S Cal
It looks like you have one of these

attachment.php



You should be able to just replace it with something like this.
attachment.php


They are both designed to fit into a 'single gang' box like this, unless your builder did something funky

attachment.php


But, some sort of adapter like I posted would work fine and is probably your easiest solution...

The outlet on the wall behind the shelves - check to see if that is perhaps a GFCI outlet just for curiosity sake
 

Attachments

  • TRI -056.jpg
    TRI -056.jpg
    76.9 KB · Views: 313
  • TRI -055.jpg
    TRI -055.jpg
    136.9 KB · Views: 315
  • TRI -057.jpg
    TRI -057.jpg
    125.2 KB · Views: 313

acer66

Well-known member
Joined
Dec 4, 2010
Messages
4,418
Location
Western North Carolina
You could have just one gfci receptacle somewhere in there protecting the whole garage.

My folks have a house build in ‘92 where they (builder) hooked up an exterior receptacle to the gfci in the bathroom.

If you want to work on electric it might help to get a tester that is able to trip gfcis.
 
OP
M

mrhul

Member
Joined
May 5, 2018
Messages
10
You could have just one gfci receptacle somewhere in there protecting the whole garage.

My folks have a house build in ‘92 where they (builder) hooked up an exterior receptacle to the gfci in the bathroom.

If you want to work on electric it might help to get a tester that is able to trip gfcis.

I just checked freeze gfci and I found out it is on a separate circuit. I was not able to locate any other gfci outlet in the garage.
 
OP
M

mrhul

Member
Joined
May 5, 2018
Messages
10
Ok, it looks like you want to install some sort of smart/wifi remote for your garage door?

attachment.php


Sometimes people on Garage Journal can get carried away with the things... If I was in your shoes, I would just change out the current receptacle and add a standard duplex, or even easier would be to just add an adapter like this.

attachment.php

I am started to lean towards adapter now.. as there are unanswered questions on GFCI outlet.
 

Git

Well-known member
Joined
May 18, 2008
Messages
6,894
Location
S Cal
mrhul -> Couldn't help but notice this door opener remote is on sale at Amazon - $20 off, coupon on the web page

attachment.php
 

Attachments

  • TRI -096.jpg
    TRI -096.jpg
    107.6 KB · Views: 116
OP
M

mrhul

Member
Joined
May 5, 2018
Messages
10
Thanks Git.. I bought two. Again thanks for all the help from everyone :)
 