Hello!
I’ve been searching the internet for information / videos on this process for quite some time and have yet to come up with solutions so I’m hoping for assistance! I am installing a garage heater in my garage and have a vertical vent kit that needs to pass from the heated space, into the attic which has cellulose insulation blown into it and terminating out of the roof. The items I have are listed below followed by my specific questions.
Heater: Mr. Heater MHU80NG (F260560)
Vent Kit: Mr. Heater 4” vertical vent kit (F102848)
Vent kit includes:
(qty 1) 4 x 36 in. B vent pipe
(qty 2) 4 x 24 in. vent pipes
(qty 1) 4 in. 90° elbow
(qty 1) wall firestop
(qty 1) roof flashing
(qty 1) storm collar
(qty 1) vent cap
My issues/questions
1) Termination point for single wall vent to B-vent. Can this occur near the top of the attic space just before the pipe goes outside? Or does this have to happen prior to entering the attic space? I was only supplied with a single B-vent which would only reach the top roof flashing due to code for exterior requirements as explained in step 4. Essentially trying to figure out if I need to purchase more B-vent.
2) Wall firestop – this piece of steel is essentially useless unless I’m using B-vent through it from what I can tell. Code requires 6” of clearance around single wall vent and there is only approximately 2” of steel on 2 of the sides of the hole. So I believe that I cannot use this piece for attic stability unless I’m using the b-vent. Is that correct?
3) Assuming that I can use the Single wall vent into the attic, can I purchase 2x 24”x24” 26 gauge galvanized steel sheets and use a hole cutter to cut 4-1/8” holes in them and attach one to the bottom of the ceiling (removing the drywall and securing to the joists / framed box that I’ll make to keep insulation out). And then building a plywood box higher (approx. 12” tall) to maintain the air gap above the insulation and attach the 2nd plate up there for the vent pipe to pass through and keep insulation out? From videos online it appears as if you can make a vent box in the attic out of plywood / OSB as long as you keep the minimum clearances. 6” for Single wall and 2” for B-vent?
4) As for termination outside, I’m going with the guide which showed 3 ft from the HIGH side of the roof flashing as the minimum vertical height and 10 ft from the pipe to the point on the roof 2 ft down from the top of the b-vent. I have a 6/12 slope so unfortunately that ends up with a calculated value of 7 ft of b-vent.
I have to measure, but I think I can use the 2nd alternative which is 3ft minimum and 2 ft above the ridge cap. I’ll go into the attic soon and measure from the hole to the ridgeline to check.
With that in mind, at what height to I need to purchase some sort of bracing for the piping?
5) Do I just use 3x screws to screw the single wall vent to the other single wall vent and to the B-vent? Are there any concerns with putting screw holes into the vents or not?
Any assistance is appreciated since the instructions are basically useless.
Thanks,
I’ve been searching the internet for information / videos on this process for quite some time and have yet to come up with solutions so I’m hoping for assistance! I am installing a garage heater in my garage and have a vertical vent kit that needs to pass from the heated space, into the attic which has cellulose insulation blown into it and terminating out of the roof. The items I have are listed below followed by my specific questions.
Heater: Mr. Heater MHU80NG (F260560)
Vent Kit: Mr. Heater 4” vertical vent kit (F102848)
Vent kit includes:
(qty 1) 4 x 36 in. B vent pipe
(qty 2) 4 x 24 in. vent pipes
(qty 1) 4 in. 90° elbow
(qty 1) wall firestop
(qty 1) roof flashing
(qty 1) storm collar
(qty 1) vent cap
My issues/questions
1) Termination point for single wall vent to B-vent. Can this occur near the top of the attic space just before the pipe goes outside? Or does this have to happen prior to entering the attic space? I was only supplied with a single B-vent which would only reach the top roof flashing due to code for exterior requirements as explained in step 4. Essentially trying to figure out if I need to purchase more B-vent.
2) Wall firestop – this piece of steel is essentially useless unless I’m using B-vent through it from what I can tell. Code requires 6” of clearance around single wall vent and there is only approximately 2” of steel on 2 of the sides of the hole. So I believe that I cannot use this piece for attic stability unless I’m using the b-vent. Is that correct?
3) Assuming that I can use the Single wall vent into the attic, can I purchase 2x 24”x24” 26 gauge galvanized steel sheets and use a hole cutter to cut 4-1/8” holes in them and attach one to the bottom of the ceiling (removing the drywall and securing to the joists / framed box that I’ll make to keep insulation out). And then building a plywood box higher (approx. 12” tall) to maintain the air gap above the insulation and attach the 2nd plate up there for the vent pipe to pass through and keep insulation out? From videos online it appears as if you can make a vent box in the attic out of plywood / OSB as long as you keep the minimum clearances. 6” for Single wall and 2” for B-vent?
4) As for termination outside, I’m going with the guide which showed 3 ft from the HIGH side of the roof flashing as the minimum vertical height and 10 ft from the pipe to the point on the roof 2 ft down from the top of the b-vent. I have a 6/12 slope so unfortunately that ends up with a calculated value of 7 ft of b-vent.
I have to measure, but I think I can use the 2nd alternative which is 3ft minimum and 2 ft above the ridge cap. I’ll go into the attic soon and measure from the hole to the ridgeline to check.
With that in mind, at what height to I need to purchase some sort of bracing for the piping?
5) Do I just use 3x screws to screw the single wall vent to the other single wall vent and to the B-vent? Are there any concerns with putting screw holes into the vents or not?
Any assistance is appreciated since the instructions are basically useless.
Thanks,