To begin with I have searched and searched and was not able to find an answer so here goes. I am installing a 50k mr heater in my garage. I am doing a horizontal vent. Everyone I know vented with standard b vent horizontal . I realize that is not correct so I opted for the stainless class III vent kit. B vent clearance to combustibles is 1 inch. The stainless class III single wall also says 1 inch. This does not seem correct to me considering the single wall will get much hotter. Am I missing something here ? Thanks in advance
 
To avoid these ads, REGISTER NOW!
OP
N

Ntandro

New member
Joined
Nov 19, 2019
Messages
4
Location
Chicago
Yes b vent is the double wall. But everywhere and everyone says don’t use that for horizontal venting
 

pbon

Well-known member
Joined
May 14, 2017
Messages
3,498
What are you having trouble maintaining clearance from? The stainless horizontal does not get very hot so 1 inch should be fine.
 

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
Last edited:

k-os

Well-known member
Joined
Dec 29, 2012
Messages
995
Location
WI
Get a wall thimble to use with the CAT III vent. That will satisfy the combustible clearances.
 

Showkey

"MEMBER EMERITUS"
Joined
Aug 9, 2014
Messages
8,638
Location
Wausau WI
Get a wall thimble to use with the CAT III vent. That will satisfy the combustible clearances.

That only satisfies the wall penetrations ......... clearance to the entire vent system still has to be observed.
 

k-os

Well-known member
Joined
Dec 29, 2012
Messages
995
Location
WI
That only satisfies the wall penetrations ......... clearance to the entire vent system still has to be observed.
Right, I should have expanded to say that the thimble will handle the clearances through the wall.

Sent from my PH-1 using Tapatalk
 
To avoid these ads, REGISTER NOW!
OP
N

Ntandro

New member
Joined
Nov 19, 2019
Messages
4
Location
Chicago
Yea I read them and 1 inch is what I saw. But didn’t seem right because b vent clearance is 1 inch and it’s double wall. So why would double wall b vent and single wall stainless have the same clearances
 
OP
N

Ntandro

New member
Joined
Nov 19, 2019
Messages
4
Location
Chicago
Nothing is closer than an inch. And why question the manufacturer? Take a look at their manuals and you’d know why. If it doesn’t make sense I look for further answers
 

pbon

Well-known member
Joined
May 14, 2017
Messages
3,498
Let us know what you find out, but it sounds like there is no problem you need help solving and this is more of a theoretical question. Have you tried Google? Installation manuals are not always accurate or well written.
 

racin72charger

Well-known member
Joined
Mar 22, 2015
Messages
161
Location
Hamilton, Ont.
What I’m doing is b vent through the wall via a thimble and vertically once it’s outside past the peek of my roof. No way in hell am I going to cut a hole in my steel roof.
 

Bretny

Well-known member
Joined
Jul 31, 2017
Messages
3,918
Location
Dutchess county NY
A metal roof is actualy easier to patch than shingles. Idk why people make such a big deal about it. There pannels, remove the screws and it comes right off.
 

pbon

Well-known member
Joined
May 14, 2017
Messages
3,498
What I’m doing is b vent through the wall via a thimble and vertically once it’s outside past the peek of my roof. No way in hell am I going to cut a hole in my steel roof.

What you are doing probably is not to code since it appears the exhaust is horizontal until outside of the building and code requires double wall stainless. But code does not matter to many people. Until 8 years ago, code allowed horizontal b vent.
 