Garage heating decisions / dilemma

tmshort

Well-known member
Joined
Dec 10, 2012
Messages
396
Location
Central IN
All-

Yet another heating / cooling question. Here are the basics:

Central Indiana. Detached shop. 24x36 on the ground, concrete slab. Walls are 2x4 with R-13. No windows downstairs, 2 exterior doors and 2 insulated overhead garage doors. 10' ceilings. The shop is of a gambrel roof design, and there is finished upstairs space which I would like to heat as well. It is insulated with R-19 in the 2x6 space between the sheetrock and the roof. There are several windows upstairs. There is an open stairway in the corner which leads to this space, so it is fairly contiguous with the downstairs.

I did not build this - came with the house. I would have insulated better, but it has pretty standard R-13 and 19 in the walls / ceiling. I have some work to do on sealing the doors / windows.

Last winter I heated with a 10kW electric heater which I installed (shop has its own 200A service). I have a wifi t-stat to control it, and keep it around 44F when I am not there. Electricity runs about 0.08+/kwh. The unit is downstairs. We had an unusually cold winter last year, and I spent some serious cash heating the place. Plus, it takes a long time for the 10kW heater to heat the place up to a comfortable temp for working.

I live in the country - no natural gas available. I have a 500 gal propane tank buried elsewhere on the property, but it is 300'+ away from the shop, with obstacles in between (house, pool, etc).

I've considered the following options and would like thoughts / input:

- mini split system.
- the good here is that the new ones are efficient. I would also have AC for the summer, but the shop stays pretty cool as it is tucked along the N side of the woods and well shaded. I don't do as much indoor work in the summer, as I am busy outside with garden / orchard etc.
- another benefit is the use of a dual system, with one unit upstairs and one downstairs to even out temps
- I can do the install, but it is not something I have done and there would be some learning curve.

- propane forced air
- I've looked at the Modine high efficiency forced air units (http://www.modinehvac.com/web/Greenhouse/Greenhouse-Heating-Solutions/Effinity93-High-Efficiency-Gas-Fired-Unit-Heater.htm#.VG2xZdLF9SA) which seem great, easy to install, vent through PVC.
- downside here is that I'd need another propane tank. Have not looked into costs of rental vs purchase, etc.
- I'm not exactly sure what size; I've run all kinds of calculators online, and am guessing at the 85,000 BTU unit. Any thoughts?
- Is there any downside to the units that have a sealed combustion chamber? Does using outside air decrease the overall efficiency of the unit? Just wondering if pulling in 0F air affects how well the heater can heat the inside of the building.

Thanks in advance for any thoughts / analysis. I'd be interested to hear what you all think about sizing, type of heat, etc. The 10kW heater I have works, but it takes a couple of hours to get up to temp, and is undersized for what I need.
 
To avoid these ads, REGISTER NOW!

CNGsaves

Well-known member
Joined
Sep 26, 2012
Messages
13,233
Location
KS and OK
Sounds nice !! Can you post up some PICS . . . .
. . . gives best chance to obtain advice suited to your garage.

Also forgot . . . Welcome to GJ !! :beer:

No guru here, but at face value your idea of 85K Btu heater that is 93% efficient sounds like way overkill for 24'x36' insulated garage. 60K or 75K would likely be sweetspot.

You are confused about SEPARATE Combustion . . . purpose is to use clean air without fumes/dust that are inside garage (thus draw in outside clean air to burn). If you plan on doing lots of woodworking, painting with fumes, staining wood, etc. then definitely need Separate Combustion. For normal garage functions, the normal heater would be fine. Top brands are Reznor, Modine (your 93% Effinity, or 80% efficient Hot Dawg), Sterling Garage Guy heater, Mr Heater Big Maxx, and Beacon Morris at Menards.

The 300 ft to your LPG tank at house is problem. Likely more cost effective to install own propane tank at garage of say 150 or 200 gallon, depending on how hot you'll keep the garage all winter. Just buy the tank and don't get snookered into lease from LPG company.
 
Last edited:
OP
T

tmshort

Well-known member
Joined
Dec 10, 2012
Messages
396
Location
Central IN
Thanks!!

- so the separate combustion is just the air used to burn the propane ... the actual heated air still comes from the inside. Duh - I guess that makes sense!! I should have thought of it! I do enough woodworking and fume generating stuff that it's probably a good idea.
- I based the 85K BTU on the fact that I'm trying to indirectly heat the upstairs as well - I appreciate any other input or thoughts on sizing.
- What recommendations do you have re: tank size?

Thanks
 
To avoid these ads, REGISTER NOW!

finn

Well-known member
Joined
Mar 27, 2005
Messages
16,609
Location
The UP, God's country
I'd like to get some of that $,08 electric here, as we're at $,27 kw/hr. I doubt that a minisplit is going to save any money if your rates are that low.

300 feet doesn't sound unreasonable to run an additional gas line.

I had the propane company run an additional line to my shop when they installed the tank for the house. The first 30 feet was free and then it was a dollar or two per foot.

The alternative was to go with a second tank, which is an ongoing rental fee or large upfront cost.
 