I have a Detached Garage 24x48 that Im looking to make a nice man cave we can hang out in year round. It has soffit vents and 2 roof vents.
I closed up all the vents with foam board and spray foam thinking I would keep hot and cold air out. All the reading I've done I might have made a mistake. Some people say add baffle vents and let it vent and others say close it all off so Im really confused a
nd need help. Whats the best way to approach this?
New York Zone 4
One Section has a cathedral ceiling roof and the rest has a ceiling. There is a little loft up top for storage.
Roof is 2x8 so I have 7.25 inches of room.
I was thinking doing R13 in all the wall stud bays.
Doing 1 inch roam board in the roof and spray foam the edges to air seal and then adding R19 faced pointing to living area on to the foam board.
Can I add fiberglass onto foam boards with out having condensation issues?
Is that enough insulation for the roof?
Thanks
Bill
I closed up all the vents with foam board and spray foam thinking I would keep hot and cold air out. All the reading I've done I might have made a mistake. Some people say add baffle vents and let it vent and others say close it all off so Im really confused a
nd need help. Whats the best way to approach this?New York Zone 4
One Section has a cathedral ceiling roof and the rest has a ceiling. There is a little loft up top for storage.
Roof is 2x8 so I have 7.25 inches of room.
I was thinking doing R13 in all the wall stud bays.
Doing 1 inch roam board in the roof and spray foam the edges to air seal and then adding R19 faced pointing to living area on to the foam board.
Can I add fiberglass onto foam boards with out having condensation issues?
Is that enough insulation for the roof?
Thanks
Bill