garage outlet

mobetta

Well-known member
Joined
Feb 10, 2010
Messages
370
Location
twin cities, mn
That will not work properly. A GFCI needs all three wires connected to it, with white and black from the panel going to the "LINE" side connections (it will be marked that way) ground to the ground screw, and all downstream receptacles black and white come off of the opposite set of connections, with the ground crimp-bonded to the end of the ground wire on the GFCI.
The lack of ground on the GFCI is probably what trips it.

not to confuse the OP, but I dont think this is correct. AFAIK, a GFCI is the only way to put a "grounded" outlet in place of a polarized outlet(2 prong, no ground) ONLY if you use the "No Equipment Ground" sticker. so the ground wire not being attached is most likely NOT the reason for the OP's problems.
 
To avoid these ads, REGISTER NOW!

Steevo

Well-known member
Joined
Aug 18, 2009
Messages
8,738
Location
43.49600, -112.04300
not to confuse the OP, but I dont think this is correct. AFAIK, a GFCI is the only way to put a "grounded" outlet in place of a polarized outlet(2 prong, no ground) ONLY if you use the "No Equipment Ground" sticker. so the ground wire not being attached is most likely NOT the reason for the OP's problems.

It is an outlet in a garage, in a house built in 2003. It had better not be a two-wire, un-grounded receptacle :)
 

smilezrcool

Member
Joined
Dec 12, 2010
Messages
16
It is sort of odd that who ever wired the outlet did not connect the grounding wire to the GFCI.
 

MrMark

Well-known member
Joined
Jan 25, 2010
Messages
4,626
Location
Southern Cal.
The GFI doesn't need the ground to work. The GFI measures the current flowing through it and checks to see that all the current flowing through it is coming back on the neutral wire as it should. If it sees return current "missing", this is "a fault condition", and it will trip.
 

smilezrcool

Member
Joined
Dec 12, 2010
Messages
16
Yes I know that a GFCI does not need a grounding conductor attached to it to make it function properly and that you can install a GFCI in place of a two wire receptacle but whoever wired the house or garage should have done the work in a "workman like manner".
 

MrMark

Well-known member
Joined
Jan 25, 2010
Messages
4,626
Location
Southern Cal.
Maybe they just grounded the box and relied on the screws in the strap to ground the strap. I haven't followed this that closely because the pictures were so screwed up but some receptacles are self grounding by listing and even though I would connect the wire, you don't always need to.
 
To avoid these ads, REGISTER NOW!

smilezrcool

Member
Joined
Dec 12, 2010
Messages
16
Yes, you are correct, it is hard to say. Maybe they used a metal box, but I hope if it is plastic they would have taken the time to ground any and all receptacles. I am not sure if all of our advice has helped or co-member?
 
OP
2

26modelt

Member
Joined
Dec 21, 2010
Messages
18
i havent got around to tryin out the ideas,,workin shift work,,,but ill put the line wire on top and the downstream wires on bottom,,maybe this is the reason my outlets on the front and back porch dont work...

and the outlet box is plastic not metal!!!

thanks guys
 
OP
2

26modelt

Member
Joined
Dec 21, 2010
Messages
18
alright guys i got it working...also the outlets on my front and back porch work also...

the group of wire was wired in on the line connection and the line wire was wired in on the downstream side,,,so i just switched the wires around and bam ,,,it worked....thanks for ur help,,,saved me some money....i owe all u guys brownies,,,and these are special brownies,,,
 
To avoid these ads, REGISTER NOW!