Garage power time

flan

Well-known member
Joined
Feb 3, 2016
Messages
427
Hello GJ after a year and a half of procrastination I’m going to run some juice out to my new detached garage. I have a 200 amp main panel in my house basement (which is on the left front corner), and the garage is detached, 25’ off the right side of the house. So I will have to run out of my main panel, across the unfinished basement, then underground 25’ to the garage where I will put in a sub panel. Total run less then 100’. I read a lot of posts that suggest 2224 MHF but it must be in conduit indoors. I have conduit run underground to the garage already so that’s no issue. Is there a better choice then MHF so I do not have to run conduit in my basement and do not have to splice before going through the conduit out to the garage? As far as loads I will be doing nothing crazy out there, light welding, 2 post lift maybe some plazma cutting, compressor, one man show won’t be using all at the same time type thing. I figured from posts on here run the 2 gauge aluminum wire to a 60 amp breaker for the possible added capacity in the future. Anyhow wire is the first up item what do you all suggest?
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
The number 2 was invented for this. Look at the value pak panels , about 65$ for 20 space main breaker, again ideal. You can use a 60 in the main. I have done a couple dozen of these,,, NEVER had one trip up a 60.
 

pattenp

Well-known member
Joined
Jun 4, 2008
Messages
10,175
Location
Virginia - USA
If you don't want to use conduit inside you don't have much choice but to splice and use SER for the inside. The only cable I can think of that doesn't need conduit inside and can go underground other than UF is AlumaFlex™ Type MC Feeder PVC Jacketed cable, but I believe the smallest it comes is 1/0 in Al.

Edit: You can get Armorlite® Type MC PVC Jacketed cable in copper in #3 which is good to 100A. https://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet162

What size conduit did you use to garage? The Armor cable may be a pain to pull through.



*
 
Last edited:

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
I used MHF, fused at 70A. No issues. I showed my inspector/AHJ the ratings on the Southwire cable I used and asked if I could run it in free air across the house attic - "no problem".
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
I used MHF, fused at 70A. No issues. I showed my inspector/AHJ the ratings on the Southwire cable I used and asked if I could run it in free air across the house attic - "no problem".

Inspector was wrong.

MHF does not have an outer jacket and therefore is required by code to be ran in conduit.
 
OP
F

flan

Well-known member
Joined
Feb 3, 2016
Messages
427
The number 2 was invented for this. Look at the value pak panels , about 65$ for 20 space main breaker, again ideal. You can use a 60 in the main. I have done a couple dozen of these,,, NEVER had one trip up a 60.

Good to hear do any of the box stores carry the value pack panels? Specific brand/model #? Will it need a main breaker?

If you don't want to use conduit inside you don't have much choice but to splice and use SER for the inside. The only cable I can think of that doesn't need conduit inside and can go underground other than UF is AlumaFlex™ Type MC Feeder PVC Jacketed cable, but I believe the smallest it comes is 1/0 in Al.

Edit: You can get Armorlite® Type MC PVC Jacketed cable in copper in #3 which is good to 100A. https://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet162



What size conduit did you use to garage? The Armor cable may be a pain to pull through.



*

2 1/2” to make pulling easier. Maybe mhf will be the way to go, conduit is cheaper then the more expensive copper.

I used MHF, fused at 70A. No issues. I showed my inspector/AHJ the ratings on the Southwire cable I used and asked if I could run it in free air across the house attic - "no problem".

Interesting, that goes against what most have said here in the past since it’s individual conductors without a sheathing...
 
Last edited:

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,317
Location
Alexandria, VA
I ran 2-2-2-4 AL MHF from the garage panel up to the house in 2" conduit, and through the house wall to a 12"x12" junction box. I then spliced to 2-2-2-4 AL SER and ran that across the basement to the panel. I used a 60 amp breaker just because I could get one off-the-shelf at HD. I also decided to buy the expensive insulated connectors (Polaris?) to splice large gauge wire, since I only needed four. I found them on Amazon, and I think it was about $15/connector.

I used a 12"x12" junction box because I found a reference that said for large gauge wiring the junction box size was determined by the conduit size, not the number of wire splices or the gauge of the wire. It was a lot bigger box than I thought I needed, but did give me plenty of space to make the splices.

Bruce
 

bobdole4u2

Member
Joined
Nov 11, 2018
Messages
24
Location
dothan, al
Aluminum just for the price? I'd bump up to copper just because it's a one-time job, safer, and thinner per ampacity. 2-2-2-6 service entrance cable to a 100 amp sub panel and you'll be set for a lift, welders, plasma cutter, wood tools, etc. And you'll be safer, no noalox to deal with

Sent from my SM-G930V using Tapatalk
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
1 1/2 inch minimum for 2 alum and 2 inch is a bit easier to go thru LB's. Price goes way up past 2 and you don't need it. Box ko's are a problem as is drilling any holes in larger sizes.
Good to hear do any of the box stores carry the value pack panels? Specific brand/model #? Will it need a main breaker?
Yes, you need a main. They often have 20 and 24 space panels and the main difference is about 4 inches in length. Either works and the 24 comes with a couple more breakers but its a cost wash, even money. I use the 20 in garages and the 24 is ideal in modest homes with 100A service. This is Homeline,,, I forget the model numbers but saw both on the shelf at a Lowes a while back. I use a different panel but I started out way before Hom was a *********, today they are common in almost every store that sells electric and are priced right. I tend to use 60 in the main panel feeding these, its simply that I keep one on hand and after 60 the price goes up. I have never tripped a 60 feeding a common garage. The 2 alum wire leaves some headroom if it would ever happen, helps prop up voltage for a bit longer runs and for motor starts.
You need to add a ground bar kit to the shopping list for that panel. they have them in 20 and 24 I think, either fits. The run is from a 60 breaker,,, not to it,, the panel has a 100 main.
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
Aluminum just for the price? I'd bump up to copper just because it's a one-time job, safer, and thinner per ampacity. 2-2-2-6 service entrance cable to a 100 amp sub panel and you'll be set for a lift, welders, plasma cutter, wood tools, etc. And you'll be safer, no noalox to deal with

Sent from my SM-G930V using Tapatalk

safer than what? :headscrat
 
OP
F

flan

Well-known member
Joined
Feb 3, 2016
Messages
427
So Lowe’s by my house is closing so everything in the store is 10% off I picked up conduit to run the MHF in also picked up a 100 amp panel, ground bar kit, 2 ground rods, 60 amp breaker, some 20’s and 15’s, boxes, etc...good start for now I will be along with a few other questions along the way I’m sure. Thanks for the input it’s been helpful.
 

Attachments

  • D78D391C-2A83-4CBE-B422-AE28FB33534F.jpg
    D78D391C-2A83-4CBE-B422-AE28FB33534F.jpg
    128.4 KB · Views: 39
OP
F

flan

Well-known member
Joined
Feb 3, 2016
Messages
427
So wondering how this looks? Sorry for the 90’s Microsoft paint, it’s what I have:bounce: I didn’t put it on the picture but green bonding screws are removed from all neutral bars.
 

Attachments

  • 77298C92-8635-4680-B8C0-8B6BA9349A48.jpeg
    77298C92-8635-4680-B8C0-8B6BA9349A48.jpeg
    80.1 KB · Views: 67

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
So wondering how this looks? Sorry for the 90’s Microsoft paint, it’s what I have:bounce: I didn’t put it on the picture but green bonding screws are removed from all neutral bars.

couple of things

The ground bar on the subpanel SHOULD be bonded to the enclosure. you wrote unbonded.

Its the neutral bar in the subpanel which should not be bonded.

Also, if you put in a second ground bar in the subpanel on the right it will help keep the panel a little less cluttered

and finally, you couldve saved yourself the time used on MS paint by checking out the drawings on the Electrical FAQ sticky here:

https://www.garagejournal.com/forum/showthread.php?t=356460
 
Last edited:
To avoid these ads, REGISTER NOW!

Bretny

Well-known member
Joined
Jul 31, 2017
Messages
3,918
Location
Dutchess county NY
You also dont put a new ground rod at the garage. Only one at the main it needed.

I did SER, junction box then some kind of DB wire for my 100a in the garage. I beleive its about 175ft from main to sub pannel.
 
OP
F

flan

Well-known member
Joined
Feb 3, 2016
Messages
427
couple of things

The ground bar on the subpanel SHOULD be bonded to the enclosure. you wrote unbonded.

Its the neutral bar in the subpanel which should not be bonded.

Also, if you put in a second ground bar in the subpanel on the right it will help keep the panel a little less cluttered

and finally, you couldve saved yourself the time used on MS paint by checking out the drawings on the Electrical FAQ sticky here:

https://www.garagejournal.com/forum/showthread.php?t=356460

Thanks for the reply. I did use the sticky but wanted to make sure the way I tied in the ground and neutral going out to the garage sub panel was acceptable. The garage is a sub-sub panel I suppose. In my rendering the right panel is the 200a main panel. The one on the left is a sub directly off of it. The garage panel comes off the left (sub)


The ground bar on the first sub is one of the add on bars and is attached to the metal panel. The neutral bars (main and sub) had the green screws removed.
 
OP
F

flan

Well-known member
Joined
Feb 3, 2016
Messages
427
You also dont put a new ground rod at the garage. Only one at the main it needed.

I did SER, junction box then some kind of DB wire for my 100a in the garage. I beleive its about 175ft from main to sub pannel.

The garage is detached, I put 2 ground rods in.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,752
The best choice in panels is whatever your house panel is unless it’s a obsolete make but is a moot point since have a GE already, at least it’s not a s**t panel like Eaton BR.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
You also dont put a new ground rod at the garage. Only one at the main it needed.

I did SER, junction box then some kind of DB wire for my 100a in the garage. I beleive its about 175ft from main to sub pannel.

this is incorrect for detached structures.

ALL detached structures are required to have grounding electrodes. If using ground rods, code requires 2 spaced 6' apart.

Thanks for the reply. I did use the sticky but wanted to make sure the way I tied in the ground and neutral going out to the garage sub panel was acceptable. The garage is a sub-sub panel I suppose. In my rendering the right panel is the 200a main panel. The one on the left is a sub directly off of it. The garage panel comes off the left (sub)

The ground bar on the first sub is one of the add on bars and is attached to the metal panel.

ok, well on your diagram you have it labeled that the ground bar is unbonded. IF it is attached to the metal panel and not isolated then it IS BONDED. so your note on the diagram is incorrect.

The neutral bars (main and sub) had the green screws removed.

This may be incorrect for the main panel dependent on your setup.

What is before the main panel? Just a meter? or a meter and disconnect?
If the former, then you most assuredly should have the neutral bar bonded otherwise breakers will not be able to clear ground faults.

The neutral bar in main service panels are ALWAYS bonded.

A panel is NOT the main service panel if there is a panel or disconnect before it.
 
OP
F

flan

Well-known member
Joined
Feb 3, 2016
Messages
427
this is incorrect for detached structures.

ALL detached structures are required to have grounding electrodes. If using ground rods, code requires 2 spaced 6' apart.



ok, well on your diagram you have it labeled that the ground bar is unbonded. IF it is attached to the metal panel and not isolated then it IS BONDED. so your note on the diagram is incorrect.



This may be incorrect for the main panel dependent on your setup.

What is before the main panel? Just a meter? or a meter and disconnect?
If the former, then you most assuredly should have the neutral bar bonded otherwise breakers will not be able to clear ground faults.

The neutral bar in main service panels are ALWAYS bonded.

A panel is NOT the main service panel if there is a panel or disconnect before it.
That was wrong terminology on my part, I was thinking bonded, as in bonded to the neutral bar. So yes, the ground bar is bonded to the sub panel.

As far as the main panel (right) the service goes into the meter box on the exterior of the house then from there into the main panel. I looked yesterday and saw the ground screw sitting on the bottom of the box, same as the sub panel along side of it. Incorrect?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
That was wrong terminology on my part, I was thinking bonded, as in bonded to the neutral bar. So yes, the ground bar is bonded to the sub panel.

As far as the main panel (right) the service goes into the meter box on the exterior of the house then from there into the main panel. I looked yesterday and saw the ground screw sitting on the bottom of the box, same as the sub panel along side of it. Incorrect?

yeah that is incorrect since all you have ahead of the main panel is a meter.

The neutral bar needs to be bonded to the enclosure.

Can you take a picture of your main with the cover off?
 
OP
F

flan

Well-known member
Joined
Feb 3, 2016
Messages
427
yeah that is incorrect since all you have ahead of the main panel is a meter.

The neutral bar needs to be bonded to the enclosure.

Can you take a picture of your main with the cover off?

Sure will, I will post it tomorrow. Come to think of it a service rated automatic transfer switch for generac generator is in between the meter and main panel. Not sure if that makes a difference either way.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
Sure will, I will post it tomorrow. Come to think of it a service rated automatic transfer switch for generac generator is in between the meter and main panel. Not sure if that makes a difference either way.

Well yeah that makes a huge difference.

Thats why i asked if there was anything between the "main" panel and the neter.

Since you have an ATS, what youre calling the main is NOT a main. It is a subpanel because the ATS is your main service panel.

So leave the neutral in the "main" unbonded as it is right now.
. And lets call the "maim" what it is, a subpanel, to stop the confusion.
 

Bretny

Well-known member
Joined
Jul 31, 2017
Messages
3,918
Location
Dutchess county NY
Ground rods at detached scructures is new to me. I ran 4 conductor to mine so i get the ground from the main.

Wouldnt you create a ground loop adding ground rods and only useing 3 conductor to a detache scructure?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,983
Location
Modesto, CA
Ground rods at detached scructures is new to me. I ran 4 conductor to mine so i get the ground from the main.

The issue here is youre confusing different types of grounding.

Grounding electrodes main purposes are for grounding lightning and limiting voltage potential to earth.

EGCs/grounds on the other hand are for creating a low impedance fault current pathway so breakers can trip.

They also prevent metallic pathways such as plumbing and frames of appliances and motors from becoming energized.

2 completely different animals. NEVER confuse one for the other.

You need both for detached structure fed from another structure.

Theres a write up on exactly how to do this on the FAQ sticky. see #3.

https://www.garagejournal.com/forum/showthread.php?t=356460

Wouldnt you create a ground loop adding ground rods and only using 3 conductor to a detached structure?

no you wouldnt because of what grounding electrodes do. They shunt lighting.

And 3 wire feeds to detached structures have not been allowed since 2008 code cycle
 
Last edited: