Garage sub panel checklist

signcrafter

Well-known member
Joined
May 9, 2012
Messages
12,497
Going to start the electrical in my garage shop at the new to us house. House panel is a 200 amp in the basement. Attached garage and sub panel will be about 15 feet of wire from main panel. Going to put a square d qo 24 space main breaker 100 amp sub panel in the garage. Surface mounted on the wall for ease of adding circuits as I go. Main wire will be run in the wall and come in the back of the panel.

Is 6 gauge wire good enough? Service entrance cable the correct cable? Do I need ground rods for sub panel? I will make sure the neutral bar isnt bonded and add a ground bar. Anything else I'm missing or forgetting? Thanks.
 
To avoid these ads, REGISTER NOW!

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
32,049
Location
Coronado, CA
6 gauge is not adequate for 100 Amps. Your ground rods will depend on your location and what your local AHJ requires.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,053
Location
NJ
Going to start the electrical in my garage shop at the new to us house. House panel is a 200 amp in the basement. Attached garage and sub panel will be about 15 feet of wire from main panel. Going to put a square d qo 24 space main breaker 100 amp sub panel in the garage. Surface mounted on the wall for ease of adding circuits as I go. Main wire will be run in the wall and come in the back of the panel.

Is 6 gauge wire good enough? Service entrance cable the correct cable? Do I need ground rods for sub panel? I will make sure the neutral bar isnt bonded and add a ground bar. Anything else I'm missing or forgetting? Thanks.
The first question is what are the expected simultaneous loads?
Right now many are thinking EVSE's in their future - is it 1, 2, what size/level charger(s)?

You can fit up to a 125A CB in the basement panel depending on feeder size. (125A QO CB is $$$)
At 15' of cable, larger conductors are of minimal cost.
The CB in the main panel has to be sized to protect the conductors feeding the sub panel.
Personally, I wouldn't go smaller than #6.

An attached garage won't require grd rods or a main disconnect in the sub panel.

You may find a panel with main cb on the shelf easier/cheaper than main lug panel.
4 conductors is needed and that would make it SER and not SEU cable. Aluminum SER is sufficient, copper not required.
 
OP
S

signcrafter

Well-known member
Joined
May 9, 2012
Messages
12,497
6 gauge is not adequate for 100 Amps. Your ground rods will depend on your location and what your local AHJ requires.
Not sure why I was thinking 6, it was late when I wrote it. What size is needed? Is 100 amp breaker in main panel the correct size for 100 amp sub panel?
The first question is what are the expected simultaneous loads?
Right now many are thinking EVSE's in their future - is it 1, 2, what size/level charger(s)?

You can fit up to a 125A CB in the basement panel depending on feeder size. (125A QO CB is $$$)
At 15' of cable, larger conductors are of minimal cost.
The CB in the main panel has to be sized to protect the conductors feeding the sub panel.
Personally, I wouldn't go smaller than #6.

An attached garage won't require grd rods or a main disconnect in the sub panel.

You may find a panel with main cb on the shelf easier/cheaper than main lug panel.
4 conductors is needed and that would make it SER and not SEU cable. Aluminum SER is sufficient, copper not required.
No EVs in the near future. Simultaneous loads would be a 3hp compressor if it kicks on along with whatever other machine I'm using at that time, welder, parts washer, table saw, planer, etc. I do plan on putting in a 30 amp RV hookup but it would be it wont be hooked up very often. There will be a reznor natural gas heater so that just needs electrical for the fan. And I may do a smaller AC at some point just to help with humidity in the summer. Just a 1 man shop so while there will be a bunch of equipment in there it will never be used at the same time. Just need help with wire size and breaker size.
 
OP
S

signcrafter

Well-known member
Joined
May 9, 2012
Messages
12,497
2-2-2-4 aluminum SER cable for 90A is an easy combo.
Ok looks like 2-2-2-4 is 5.99 a foot at home depot. I know I've read about the 90 amp breaker before but dont remember where and search doesnt work the best. I didnt see 90 amp breaker at depot, just 100 amp. Can I use 100 amp breaker in main panel to feed sub panel with 2-2-2-4 wire? Or do I have to order a 90amp breaker to put in main panel to feed sub?
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,073
Location
Modesto, CA
Ok looks like 2-2-2-4 is 5.99 a foot at home depot. I know I've read about the 90 amp breaker before but dont remember where and search doesnt work the best. I didnt see 90 amp breaker at depot, just 100 amp. Can I use 100 amp breaker in main panel to feed sub panel with 2-2-2-4 wire? Or do I have to order a 90amp breaker to put in main panel to feed sub?
no #2 is rated for 90a max unless youre feeding the entire load of a dwelling.
 
OP
S

signcrafter

Well-known member
Joined
May 9, 2012
Messages
12,497
My home depot has the 90amp breakers on the shelf. When I saw them I assumed there must be GJ people in the area...the 2-2-2-4 is also regularly sold out...
Mine only had 100. I'll check menards since that's where I will get the panel anyway. If not I see them online for way cheaper then the 100 amp breaker that depot wants 118 bucks for. Thanks
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,912
Location
Richmond, VA
Just bump up to 1-1-1-3 AL SER it you want 100a. At 15 feet, I wouldn't spend a lot of time fretting over wire size or special ordering breakers.

Regardless of the feed breaker, you can use any size subpanel you want.
 