I need a little help/guidance.
I need to add a few 240 outlets in my garage and my current panel is full. So I plan on adding a sub panel and need a little guidance.
Here is my main panel that has a 90 amp breaker feeding it, of course full. So I plan on consolidating four circuits into two with tandem breakers opening up space for a 50-60(?) amp breaker for the sub panel.
I want to move the sub panel down the wall closer to my bench. Mainly to save on wire cost because I want to add three 240 volt and one dedicated 120 volt outlets. All of which will be located within 5-10 feet of the proposed sub panel location.
I will add a 50 amp breaker for one outlet. For a stick welder and hopefully a cnc plasma table in the future.
I need another outlet for a plasma cutter, I think a 30 amp should cover it but I'm not sure.
I also need another outlet for an air compressor, again I think 30 amps should be good.
Then I will do a dedicated 20 amp 120v for my Lincoln 140 mig.
So my questions are:
Am I good with a 50 amp breaker to the sub panel or do I need to go bigger? The only thing that would be running simultaneously is the air compressor/plasma cutter.
The run of wire to the sub panel will be 30-35 feet. So is 6/3 appropriate for these needs and to have 240/120?
Are my estimates correct in needing 30 amp breakers for the plasma and compressor motor?
Thanks for the assistance! Hopefully I provided enough info, if not let me know what else you need.
Sent from my iPhone using Tapatalk
I need to add a few 240 outlets in my garage and my current panel is full. So I plan on adding a sub panel and need a little guidance.
Here is my main panel that has a 90 amp breaker feeding it, of course full. So I plan on consolidating four circuits into two with tandem breakers opening up space for a 50-60(?) amp breaker for the sub panel.

I want to move the sub panel down the wall closer to my bench. Mainly to save on wire cost because I want to add three 240 volt and one dedicated 120 volt outlets. All of which will be located within 5-10 feet of the proposed sub panel location.
I will add a 50 amp breaker for one outlet. For a stick welder and hopefully a cnc plasma table in the future.
I need another outlet for a plasma cutter, I think a 30 amp should cover it but I'm not sure.

I also need another outlet for an air compressor, again I think 30 amps should be good.

Then I will do a dedicated 20 amp 120v for my Lincoln 140 mig.
So my questions are:
Am I good with a 50 amp breaker to the sub panel or do I need to go bigger? The only thing that would be running simultaneously is the air compressor/plasma cutter.
The run of wire to the sub panel will be 30-35 feet. So is 6/3 appropriate for these needs and to have 240/120?
Are my estimates correct in needing 30 amp breakers for the plasma and compressor motor?
Thanks for the assistance! Hopefully I provided enough info, if not let me know what else you need.