All,
I am getting ready to run the wiring for a 100-amp subpanel in my detached garage. My question relates to grounding rods.

First question: one or two grounding rods? If two, how far apart.

Second question: Do the grounding rods need to stick out of the ground or can I attach a copper cable to them and keep them several inches below ground (so the top of the ground rod cannot be seen or tripped over).

Thanks
Jeff
 
To avoid these ads, REGISTER NOW!

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
2 rods about 10 ft or so apart, dig a small hole and pound them down out of the way, I like them under the eve where the run off water is.
 
To avoid these ads, REGISTER NOW!

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
2 rods about 10 ft or so apart, dig a small hole and pound them down out of the way, I like them under the eve where the run off water is.

They only have to be a minimum of 6' by code.

I usually dig a 6.5' trench, pound rods at each end and run one continuous #4 bare copper from one rod to the next to the panel. The top of the rods must be flush with or below ground level.
 