smokey0066
Well-known member
I just recently purchased a Tesla and I wanted to installed the wall charger in my garage. Spoke with an electrician and then I was asking them to put some extra receptacles in and then it got “complicated” as he put it. I didn’t actually get a quote back yet but I started doing a lot of reading, youtube watching, and talking to some coworkers trying to understand why it got complicated. That got me thinking I could probably put in a sub panel in the garage and wire up most of the garage myself.
What I’d like to put in are 1 wall charger and rough in for a second one. Along the perimeter I'd like to add some 120v 20a receptacles (probably 1 circuit for each side of the garage) and possibly a 240v in the corner for a future air compressor while I’m in there – not sure plug or amperage rating that I need (so please correct my shopping list if I'm mistaken). I’ll also run some ethernet to the garage while I’m in there. There is only 1 circuit feeding my garage right now which are 3x overhead light, 2x ceiling receptable for garage door opener, 1x wall receptacle which everything in the garage is plugged into. I will trip the breaker when doing a lot of work outside so I need to be mindful of the load I use right now.
Our area follows the 2020 NEC codes. My house has a 200amp CH panel on the opposite side of the garage so it’ll be a longer run. My basement and garage are both unfinished except for the shared wall which is insulated and sheet rocked on the garage side. The run from my main panel to the sub would be about 75ft depending on exact placement of the panel and wire routing. Then from the sub to the wall charger will be maybe 40ft. I'm trying to keep everything in the walls which could make my life miserable....
Shopping list:
CH 100amp breaker
SER 1-1-1-3 copper feeding the sub panel
Eaton CH subpanel Model: CHP22B100V29
CH 2 pole 60amp breaker
NM-B 4/3 copper for the tesla charger
CH 1 pole 20amp AFCI/GFCI breaker
NM-B 12/2 for the rest of the garage
CH 2 pole 30amp breaker
NM-B 8/3 for the 240 – future air compressor?
I went with the CH subpanel to match my main panel which is also a CH panel. I know I need some TR receptacles, boxes, staples, clamps for the wires going into the panels. Will probably have a bunch of trips to the store while I’m working.
Couple of questions:
Have I missed anything in my planning and shopping list?
I'm a little bit worried about the SER and 4/3 wires, will I have a horrible time running them?
Do I need any special sealant when I’m going between the house/garage and through the top plate in the garage walls?
Should I wire anything else in “while I’m in there.. “?
When I’m wiring for the rough I know I clamp the wires in the boxes and leave the 6” out and the ground pigtailed but do I connect the other end to the breaker? Or do I just leave that end taped off inside the panel but not connected yet?
TIA if you've made it through my long post. First time doing electrical work and its a lot to take in but also very interesting.
What I’d like to put in are 1 wall charger and rough in for a second one. Along the perimeter I'd like to add some 120v 20a receptacles (probably 1 circuit for each side of the garage) and possibly a 240v in the corner for a future air compressor while I’m in there – not sure plug or amperage rating that I need (so please correct my shopping list if I'm mistaken). I’ll also run some ethernet to the garage while I’m in there. There is only 1 circuit feeding my garage right now which are 3x overhead light, 2x ceiling receptable for garage door opener, 1x wall receptacle which everything in the garage is plugged into. I will trip the breaker when doing a lot of work outside so I need to be mindful of the load I use right now.
Our area follows the 2020 NEC codes. My house has a 200amp CH panel on the opposite side of the garage so it’ll be a longer run. My basement and garage are both unfinished except for the shared wall which is insulated and sheet rocked on the garage side. The run from my main panel to the sub would be about 75ft depending on exact placement of the panel and wire routing. Then from the sub to the wall charger will be maybe 40ft. I'm trying to keep everything in the walls which could make my life miserable....
Shopping list:
CH 100amp breaker
SER 1-1-1-3 copper feeding the sub panel
Eaton CH subpanel Model: CHP22B100V29
CH 2 pole 60amp breaker
NM-B 4/3 copper for the tesla charger
CH 1 pole 20amp AFCI/GFCI breaker
NM-B 12/2 for the rest of the garage
CH 2 pole 30amp breaker
NM-B 8/3 for the 240 – future air compressor?
I went with the CH subpanel to match my main panel which is also a CH panel. I know I need some TR receptacles, boxes, staples, clamps for the wires going into the panels. Will probably have a bunch of trips to the store while I’m working.
Couple of questions:
Have I missed anything in my planning and shopping list?
I'm a little bit worried about the SER and 4/3 wires, will I have a horrible time running them?
Do I need any special sealant when I’m going between the house/garage and through the top plate in the garage walls?
Should I wire anything else in “while I’m in there.. “?
When I’m wiring for the rough I know I clamp the wires in the boxes and leave the 6” out and the ground pigtailed but do I connect the other end to the breaker? Or do I just leave that end taped off inside the panel but not connected yet?
TIA if you've made it through my long post. First time doing electrical work and its a lot to take in but also very interesting.