Getting the garage organized at the new place and putting things where I think I want them to live...and discovering the electrical is not what I thought it was.
Currently I have a 50A breaker on the main panel feeding the sub with #10 wire...through 1/2" conduit. EMT is buried (about 10ft between the house and the garage, with short pieces of flex to connect to the main panel and sub.
#10 is not good for 50A. Currently, there is a 30A 240V circuit for the dryer, a 15A 240 circuit feeding an outlet (I'm not sure what good 15A of 240V is), a couple 20A 120V circuits feeding outlets and a 15A circuit for the lights.
I would like to run a 40A 240V circuit with 2 outlets...one for the dryer and one for my compressor/welders/etc, then come off of those into a couple disconnects to feed the mill and the lathe (powered by VFDs) The 120V circuits can remain intact.
I need at least #8. I can fit 3 #8s through the 1/2" conduit.
Question 1: Can I also fit a #10 bare ground along with my 3 #8s in the 1/2" conduit?
Question 2: Can I use the conduit as my ground and simply pull 2 hots and a neutral?
Currently I have a 50A breaker on the main panel feeding the sub with #10 wire...through 1/2" conduit. EMT is buried (about 10ft between the house and the garage, with short pieces of flex to connect to the main panel and sub.
#10 is not good for 50A. Currently, there is a 30A 240V circuit for the dryer, a 15A 240 circuit feeding an outlet (I'm not sure what good 15A of 240V is), a couple 20A 120V circuits feeding outlets and a 15A circuit for the lights.
I would like to run a 40A 240V circuit with 2 outlets...one for the dryer and one for my compressor/welders/etc, then come off of those into a couple disconnects to feed the mill and the lathe (powered by VFDs) The 120V circuits can remain intact.
I need at least #8. I can fit 3 #8s through the 1/2" conduit.
Question 1: Can I also fit a #10 bare ground along with my 3 #8s in the 1/2" conduit?
Question 2: Can I use the conduit as my ground and simply pull 2 hots and a neutral?