My house has a 200A panel.

I have two separate garages that are both separate buildings from the main house.

One of these buildings is new and the electrician just put in the panel, hence the questions:

The main panel at the house has a 100A 240V (2 pole) breakers for each garage. There is one for each garage.

In each garage, there is a 100A 240V (2 pole) "service disconnect"/main breaker.

Is that cool? For some reason I thought the total of the two subpanels (the garages) had to be less than the main?

C
 
To avoid these ads, REGISTER NOW!

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,589
Location
Long Island
Sounds cool to me. The sum total of breaker currents in a panel can easily add up to WAY more than the main. Don't worry about that.
 
OP
V

Vintage Veloce

Well-known member
Joined
Feb 27, 2015
Messages
1,076
Location
San Diego
Yes, I know the breakers can add up to be more. But I thought there might be something about the number of separate "sub-panels" and how those add up.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,589
Location
Long Island
Nope. There's no difference whether the breakers supply a sub-panel or machine or outlets or lighting. All that matters is that the total expected load will not exceed the main.
 

AZ Garage

Well-known member
Joined
Sep 23, 2009
Messages
82
Location
Mesa AZ
The main panel at the house has a 100A 240V (2 pole) breakers for each garage. There is one for each garage.

In each garage, there is a 100A 240V (2 pole) "service disconnect"/main breaker.

Is that cool? For some reason I thought the total of the two subpanels (the garages) had to be less than the main?

C

The total overall connected load has to be less than the Main.

Those sub-panels could both be 200A each, but as long as the total connected load on both those AND the main are less than 200A, than you're fine.

That's why load summaries on each panel are performed and submitted with electrical plans.
 
To avoid these ads, REGISTER NOW!
OP
V

Vintage Veloce

Well-known member
Joined
Feb 27, 2015
Messages
1,076
Location
San Diego
That's why load summaries on each panel are performed and submitted with electrical plans.

Interestingly, they didn't require that. They do collect a circuit card on the rough inspection, but there is no actual load information on that, just a list of the circuits installed.
 

justsam

Well-known member
Joined
Aug 20, 2010
Messages
1,267
Location
Penngrove, California
The real protection is being provided by the breakers in the main house panel. As you eluded to the pair at each sub panel is really a disconnect, which is not required at all unless there are more than 6 breakers at the sub panel.

Do you know what type and size of wire is being used to feed the sub panels, that are being fed by the 100 Amp breakers at the main panel?

Sounds like you may be an Alfa owner?
 
OP
V

Vintage Veloce

Well-known member
Joined
Feb 27, 2015
Messages
1,076
Location
San Diego
There might be an Alfa in my life. ;-)
I don't remember the wire size, except that the electrician sized it right for the current. It was fat. There's a 50A 220 circuit out there for a potential electric car charger.
 

md21722

Well-known member
Joined
Nov 30, 2015
Messages
1,840
Location
Mt Juliet, TN
This can happen all the time with mutually exclusive loads. For example, most people don't run A/C and heat at the same time. Cool on having two separate garages!
 