My Gas Furnace went out and now wont ignite again. The blower keeps running but just blows cold air. Normally you would hear a click click noise before it would light but there is nothing now... Any suggestions or tips?



The furnace is a Goodman Furnace


Thanks
 
To avoid these ads, REGISTER NOW!

jhelrey

Well-known member
Joined
Sep 15, 2010
Messages
7,254
Location
MN
Clean the flame sensor and check the hot surface igniter for cracks, etc.
 

brihvac

Well-known member
Joined
Dec 21, 2011
Messages
484
Location
North Wilmington, Delaware
Inducer starts, air switch makes, HSI glows, burner lights, blower comes on.
Do you have a multi meter? Unplug HSI, stick probes inside plug coming from the board, reset heater, and test for 110v going to it. If you have it, the HSI is bad. If you don't make sure the inducer motor is good, flue pipe is clear, air switch is making, (if 90+) make sure your condensate line is clear.
 

manrmark

Well-known member
Joined
Sep 6, 2009
Messages
75
Location
Nebraska Panhandle
I'm not expert but I would check the flame sensor. I have a York furnace about 7 years old and it would do the same as you described. It would get soot on it and I was able to remove it and clean it with a brass wire brush, I eventually replaced it.

Hopefully a HVAC person will chime in.
 
To avoid these ads, REGISTER NOW!

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
If the blower runs constantly & the t-stat is NOT set to "fan on", I'd check the fan/limit switch...

Tommy
 

larry4406

Well-known member
Joined
Jan 27, 2006
Messages
19,483
Location
Northern Virginia
Recently I have had several new Lennox units in our houses where the pressure switch for the inducer fan has failed. Unit thinks that the inducer fan is not operating properly and will not progress to the HSI and gas valve opening mode.
 

Ohmthis

Well-known member
Joined
Jan 20, 2013
Messages
3,018
Location
Outside of Louisville KY
Let's start simple. Check and change your filter, not enough air flow will cause problems. Check and clean out anything in the flue, again this will cause problems. Does your furnace have a fault light. It's a red led usually in the blower section. What is it blinking? The process of the furnace is as follows. Inducer fan comes on, about 30 sec later the hsi ingniter blows, flames comes on, main blower runs. Where does this get interrupted?
 
OP
S

SI86

Well-known member
Joined
Aug 30, 2013
Messages
71
Location
Pennsylvania
Well It was the Limit Switch.. A friend of mine came down and he ended up reseting the limit switch?? Does that sound right? What could cause a Limit switch to need reset? This was in my rental house and I have no clue how often them change the filter... they put a brand new one in before I got there so I don't know if that caused any issues. Didn't get to see the old one they took out
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
Well It was the Limit Switch.. A friend of mine came down and he ended up reseting the limit switch?? Does that sound right? What could cause a Limit switch to need reset? This was in my rental house and I have no clue how often them change the filter... they put a brand new one in before I got there so I don't know if that caused any issues. Didn't get to see the old one they took out

There's probably a reason you didn't get to see the old one.
 

southalabama

Well-known member
Joined
Jan 10, 2011
Messages
5,540
Location
Brewton AL
Cheapest first. Check flame sensor. Rub it with steel wool or sandpaper. It worked on mine when I had a similar issue. The a/c guy is a cousin and he didn't charge for doing it
 