Im looking to run a gas line to the house and garage. Meter will be at the road 1290 ft away. Was told that the main is a medium pressure and can supply at 2 psig. Specific gravity is 0.6. My load will be 200,000 btu's. I am looking at 1" cts. My charts stop at 300ft and the gas company said they cant reccomend do to liability. Pipe supplyer said the have no clue. 16" wc drop in caculation.
With some calculation i think im at 236 Cfh.
Hoping some one may know and confirm. Thanks