I have searched and didn't find a specific answer to my question. I am installing a 45,000 btu heater in my detached garage. There is already a 3/4" gas line run to the garage but my question is should I contunue with the 3/4" pipe or can I used 1/2" from the garage connection to the heater. It's about 22 feet from the valve to the heater. I plan on using black pipe.

Thanks
 
To avoid these ads, REGISTER NOW!

Junkman

Well-known member
Joined
Dec 18, 2006
Messages
6,675
Location
Northeastern CT
Not certain if it makes a difference between Natural Gas and Propane. I tend to over size when in doubt. My propane furnace would not function properly when it was extremely cold, until the gas line was replaced with a larger one. The pressures would drop when it was very cold, and the furnace would have a hard time lighting.. For the small difference in cost, I would go with the larger size.
 
To avoid these ads, REGISTER NOW!

rickairmedic

Well-known member
Joined
May 31, 2005
Messages
4,165
Location
louisville ,Ky
Junk it does make a differance propane runs at a higher pressure and needs the bigger line he will be fine on NG with 1/2" . A NG gas valve runs at 3.5" water column Propane runs closer to 13" water column .