Gas riser options

iowa4x4dieselman

Well-known member
Joined
Dec 5, 2012
Messages
224
When looking at gas risers I see 2 options. Option one is a metal riser with compression fitting on the end to transition to IPS, while the other has a short piece of IPS and would require a coupling.

Question about these is. What is the better option? or is there one? Trying to get gas from my meter to my detached garage. will have shutoff before going to the garage so if problems arise I can shut off the garage and still use gas in the house.

TIA.
 
To avoid these ads, REGISTER NOW!

HoosierBuddy

Well-known member
Joined
May 9, 2006
Messages
2,937
Location
Southern Indiana
I see no advantage to either.

If you look at them close enough you may find that they are identical other than one already has a stab coupling attached to it.

When I've been faced with this, I've been able to borrow fusion equipment from work and make my joints that way, but we have had very good success over the years with the elster permasert couplings.

Just match up your coupling size with your pipe and riser size and you should be fine. As you are aware, all of the small gas piping and fittings come in IPS (iron pipe size) and CTS (copper tube size) and they are not compatible with each other.

Phil
 
To avoid these ads, REGISTER NOW!

D45

Well-known member
Joined
Mar 21, 2014
Messages
4,836
Location
NW INDIANA
The push to lock Constab fittings are so easy to use

Just need a simple chamfer tool
 