Heys guys,

I've got a shop heater that's from 2003 that heats my barn. Recently we had a cold snap and at the same time I had the tstat set to about 67°F which is the hottest I've set it to in its life. The shop is fairly insulated but I did have a cool draft coming in due to a leaky doggy door.

The high limit switch tripped (burned up, there is no reset) and shut her down. I jumped it and it works again but I wanted to figure out why. My thought is 20 year old parts that got ran and ran harder than ever. So it gave out.

I took a temp reading and this is what I got 20240120_083342.jpg
Exhaust
20240120_083356.jpg


I have a brand new unit in my other garage and this is the reading I got from it.
20240120_083328.jpg

So I actually don't think I have an issue with my shop heater since the newer unit has more heat in the coils.

The high limit lives in the coil chamber right inbetween coils.
20240118_185947.jpg

20240118_191616.jpg
 
To avoid these ads, REGISTER NOW!

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,700
Location
Fargo, ND
I did HVAC service for years. Many times I have seen heat exchangers barely glowing red on a perfectly working units. Steel glows around 800F.

I have walked into shops with the lights off and could see the heater barely glowing red.
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
11,012
Location
Rhode Island
Those temperatures do not seem out of line at first glance. Replace the high limit switch, however. It's a critical safety device, and the temperature it trips out at will be stamped on it somewhere.

Also, the thermostat setting has no bearing on how hard the unit works. You could set the thermostat to 120°F, and the unit will work just as hard as it does if you set it to 60°F. The only thing that will change is how long it runs for.
 
OP
C

CTC DEEZUL

Member
Joined
May 10, 2014
Messages
16
Location
Indiana
Those temperatures do not seem out of line at first glance. Replace the high limit switch, however. It's a critical safety device, and the temperature it trips out at will be stamped on it somewhere.

Also, the thermostat setting has no bearing on how hard the unit works. You could set the thermostat to 120°F, and the unit will work just as hard as it does if you set it to 60°F. The only thing that will change is how long it runs for.
So with this, the unit is backed into a corner and right against the ceiling... Is there a chance that it was recirculating warmer air and the heat wasn't being extracted from the coils, causing an over temp?
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
11,012
Location
Rhode Island
I mean it's possible, but like I said, the thermostat setting has no effect on how hard the unit works. If the unit has been working in that location for years, it should be fine.

Sometimes hi limits fail. Replace the hi limit and see if it goes out again.
 
To avoid these ads, REGISTER NOW!
OP
C

CTC DEEZUL

Member
Joined
May 10, 2014
Messages
16
Location
Indiana
I've got 2 en route. I've got the heater running with the wires bypassed but I'm home for the weekend so should be good.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,700
Location
Fargo, ND
I've got 2 en route. I've got the heater running with the wires bypassed but I'm home for the weekend so should be good.
I should add, there is probably nothing wrong with the heater other than the bad limit, but how dirty is the fan blade? A little bit of dirt on the fan blades will cut the air flow a lot. It might be time to clean the blades.
 
OP
C

CTC DEEZUL

Member
Joined
May 10, 2014
Messages
16
Location
Indiana
It needs a dusting now that I've been up close.

I'm also going to run a 4 inch pvc pipe to the rear of the unit and run it maybe 20 feet down the wall so it can **** some different air.
 