Gatage Heater Issues

mtb02

New member
Joined
Jan 19, 2014
Messages
4
I have a Modine HD45AH0134 garage heater that was in the garage when we bought the house, that was one of the best parts for me!
Any ways the heater has worked great up until this year.
At first it would light then go out right away but after cleaning the flame sensor this is what it does now:

- The exhaust fan comes on
- The igniters heats up (glow red)
- The flame lights
- The blower fan comes on
- The heater runs for a minute or so
- The flame goes out (all fans still running)
- In about 30 seconds it re lights then does it all over again.
There is no error flashing on the light in the heater it is going bright dim which indicates normal, exhaust vent is clear and everything looks clean.

Does anyone have any other ideas I could try? :headscrat
Thank you
 
To avoid these ads, REGISTER NOW!
OP
M

mtb02

New member
Joined
Jan 19, 2014
Messages
4
Thanks, I'll give that a try, I just ordered the parts, it doesn't look like anyone close by deals in these parts.
 

frankush

Well-known member
Joined
Oct 23, 2011
Messages
1,156
Location
IL
Make sure your vent is not obstructed also. I agree that it's probably shutting down due to high temp in the vent. I've seen snow covered vents create the same condition.
 

RDesigns

Member
Joined
Jan 4, 2013
Messages
21
Location
Illinois
that happened a few weeks back at work. the exhaust was covered in snow due to it being on a wall above another roof the snow drifted over and covered it would blow back thru the burner tubes and shut off.
 
To avoid these ads, REGISTER NOW!
OP
M

mtb02

New member
Joined
Jan 19, 2014
Messages
4
Well the limit switch didn't fix it, or a new flame sensor, The exhaust is clear up to the cap, but I have to check when its light out to see if there is anything stuck in it on the roof.
 

sprntpshr

Well-known member
Joined
May 27, 2011
Messages
269
Location
Southern Ontario
Didn't see it but have you checked if the pressure sense line from the pwr venter to the pressure switch is clear? It may be partially blocked or the hose bib on the venter corroded.
 
Last edited:
OP
M

mtb02

New member
Joined
Jan 19, 2014
Messages
4
I jumped the thermostat tonight with no luck... Will work on it more tomorrow.
 

DenisG

Well-known member
Joined
Jul 14, 2013
Messages
1,278
Location
Milwaukee
The pressure switch is a simple switch to check for exhaust flow. You can also jumper that to see if that is the cause of the problem.
 