Location
Fairfax, VA
Any of those will be fine as a replacement and you won't go wrong by choosing the Leviton devices. Do check to see if your local jurisdiction requires tamper resistant receptacles and go that route. Also, determine if your circuit is 15 or 20 ampere and get the appropriately rated device.
 

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
>you won't go wrong by choosing the Leviton devices.

Agree - usually try to stick with that mfg and consider their parts trouble free. That GFCIs die sometimes is just a fact of life.
 
OP
J

Jsf721

Well-known member
Joined
Dec 23, 2012
Messages
4,126
Location
LI, NY
How do I determine how many AMPS the circuit is?

If I am unsure of the Amps can I just get the 20AMP GCFi's Or is that problematic?

Any of those will be fine as a replacement and you won't go wrong by choosing the Leviton devices. Do check to see if your local jurisdiction requires tamper resistant receptacles and go that route. Also, determine if your circuit is 15 or 20 ampere and get the appropriately rated device.
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Just install a 15. It only refers to the recept/plug type and you co not need 20. A 15 likely has a 15 breaker and 14 wire. A 15 can go on a 20A circuit, in fact a good share of the countries outlets are 15 unless owner installed.
 

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
How do I determine how many AMPS the circuit is?

If I am unsure of the Amps can I just get the 20AMP GCFi's Or is that problematic?

You can confirm the ckt amps by looking at the breaker feeding it. If it's a 20A breaker...then you have a 20A ckt. Of course I'd double check the wire to make sure it's 12g.

I can also understand some of your confusion.

'Typically', house ckt's are 20A service, but in almost all cases, 15A outlets are installed. Also note there is technically no limit (in the US) on how many outlets you can have installed on a 20A ckt.

You can install a 20A outlet....they are easy to recognize...they have one of the blades to the side. Unless you have a device needing 20A....use 15A outlets
 

Attachments

  • 20a Outlet.jpg
    20a Outlet.jpg
    30.4 KB · Views: 5
To avoid these ads, REGISTER NOW!
OP
J

Jsf721

Well-known member
Joined
Dec 23, 2012
Messages
4,126
Location
LI, NY
I wonder if my wifes hair IRONER is too many apms and that's why the GCFI got fried?

Any idea?

Thanks

Just install a 15. It only refers to the recept/plug type and you co not need 20. A 15 likely has a 15 breaker and 14 wire. A 15 can go on a 20A circuit, in fact a good share of the countries outlets are 15 unless owner installed.

You can confirm the ckt amps by looking at the breaker feeding it. If it's a 20A breaker...then you have a 20A ckt. Of course I'd double check the wire to make sure it's 12g.

I can also understand some of your confusion.

'Typically', house ckt's are 20A service, but in almost all cases, 15A outlets are installed. Also note there is technically no limit (in the US) on how many outlets you can have installed on a 20A ckt.

You can install a 20A outlet....they are easy to recognize...they have one of the blades to the side. Unless you have a device needing 20A....use 15A outlets
 

ddawg16

Well-known member
Joined
Jul 11, 2008
Messages
21,005
Location
S. California
I wonder if my wifes hair IRONER is too many apms and that's why the GCFI got fried?

Any idea?

Thanks

I doubt it. I'd be more inclined to think you have a bad connection...or the GFCI wore out.

Are you using pigtails inside the box?
 

TRWham

Well-known member
Joined
Aug 11, 2017
Messages
1,961
Location
East Cobb County, Georgia
To be clear, Table 210.21(B)(3) tells us you should not put a 20 A receptacle on a 15 A circuit, but you can do the reverse. There should be at least one 20 A branch circuit serving the bathroom(s), but additional, optional circuits also serving that bathroom might not be 20 A.

Regardless, no inspector is going to break down your door to check it.

ETA: the type of plug the receptacle will accept is the real difference, not the capacity of the receptacle. They don't want you plugging a 20 A load into a 15 A circuit.
 
Last edited:

snickers muncher

Well-known member
Joined
Feb 19, 2018
Messages
940
Location
Northeast GA
When I replaced the bathroom outlet I put in a GFCI with a tiny LED night light built in. That's one of the best, easy things I've done. It was a Leviton model that cost something like 2 bucks more. It's no longer made though.
 

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,320
Location
Alexandria, VA
Try to find one of the GFCI receptacles marked as "slim," since it will make it easier to fit it into the box, especially if it turns out to be a 20 amp circuit with 12 gauge wires. One like this would work https://www.homedepot.com/p/Leviton...lex-GFCI-Outlet-White-R12-GFNT2-0RW/205996739.

To be code compliant in most areas, the new receptacle should also be marked as tamper resistant, or TR, so that its harder for kids to stick anything in it and get shocked.

Bruce
 