Bought a cable to connect a generator to my home. As soon as I went to hook the cable up to ensure everything would fit, I see this (see pics, yellow highlighhts).

I would never think this would happen....but of course somethings always screwy. Anyways, anyone have a suggestion?
 

Attachments

  • IMG_20151022_165317 (Medium).jpg
    IMG_20151022_165317 (Medium).jpg
    121.4 KB · Views: 62
  • IMG_20151022_165408 (Medium).jpg
    IMG_20151022_165408 (Medium).jpg
    128.3 KB · Views: 62
  • IMG_20151022_165446 (Medium).jpg
    IMG_20151022_165446 (Medium).jpg
    112.6 KB · Views: 82
  • IMG_20151022_165450 (Medium).jpg
    IMG_20151022_165450 (Medium).jpg
    65.2 KB · Views: 113
  • IMG_20151022_165508 (Medium).jpg
    IMG_20151022_165508 (Medium).jpg
    88.2 KB · Views: 64
To avoid these ads, REGISTER NOW!
OP
O

ollie76

Well-known member
Joined
Apr 22, 2012
Messages
694
Location
Nova Scotia
Whoops, forgot to take a pic of the female end of the cable......I think you get the idea though.
 
OP
O

ollie76

Well-known member
Joined
Apr 22, 2012
Messages
694
Location
Nova Scotia
Nice catch....I should have known.

What do I gotta do to hook up a generator to this house? Every gen I look at, even in the lower 3500w range, have 30a 240v outlets.

All the cables I can find around town are 30amp ones as well.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,041
Location
Modesto, CA
Nice catch....I should have known.

What do I gotta do to hook up a generator to this house? Every gen I look at, even in the lower 3500w range, have 30a 240v outlets.

All the cables I can find around town are 30amp ones as well.

What is the size of the generator breaker in the electrical panel? Im guessing its also gonna be 20a since u have a 20a inlet.

If u want to hookup a 30a rated generator that means u would need to change to 30a rated breaker wire and inlet.

However, i doubt a 3500w 240v rated gen will have a 30a outlet because 3500w = about 15a. If u put a 30a load on it, the breaker should trip.

For 30a outlet, u would need a generator rated over 20a, such as 5100w.

What is the rating on your generator?
 
Last edited:
OP
O

ollie76

Well-known member
Joined
Apr 22, 2012
Messages
694
Location
Nova Scotia
Just checked,

30amp breaker on the main Gen.

I haven't bought one yet, luckily. We bought this home last year and all this was already in place. I'm only now getting around to getting everything set up.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,633
Location
Long Island
So you have an interlock on the panel, and a 30A breaker on the inlet?
If so, you need to confirm that you have 10 gauge wire going to the inlet, and you can swap out that inlet for a 30A one.
 
To avoid these ads, REGISTER NOW!
OP
O

ollie76

Well-known member
Joined
Apr 22, 2012
Messages
694
Location
Nova Scotia
Changed out the inlet, everything works great. Hooked up generator and tested the house on generator power only and all the essentials are powered. Pretty cool! Thanks for the help.
 

LS6 Tommy

Well-known member
Joined
Dec 27, 2013
Messages
26,162
Location
Northern NJ
My transfer panel kit had the same L14-30 connections, but it came with a short L14-30 to L14-20 adapter cable...