Generator bonding and floating neutral

sparkness

Well-known member
Joined
Nov 29, 2013
Messages
131
Location
Long Island, NY
Got a 50KW single phase generator we put it in an enclosed trailer. The use of this generator has 2 purposes. 1. power up small marina during storms. 2. Use as a portable generator. Will be stored off site.

The generator will plug into the buildings transfer switch via a pin and sleeve connector and will be a floating neutral. Inside the trailer we have a a small breaker panel. when used as a stand alone in the field we now need to bond. My thought was to use a switch to bond when used for this purpose and post clear instructions for use. any thoughts on this setup?
 
To avoid these ads, REGISTER NOW!

AA/FC

Well-known member
Joined
Dec 9, 2010
Messages
2,080
That sounds like a decent idea to me.... but I'm not a licensed electrician. When using a generator for different purposes (or different applications) it would be nice to go from a floating neutral to a bonded neutral (or vice-versa ) at the flip of a switch.
 

Chilliwack Murray

Well-known member
Joined
Dec 10, 2012
Messages
1,503
Location
Chilliwack BC
Neutral bonding is always a case by case basis (and often overlooked with temporary generators).

You need to ensure the switch you are using can carry the full fault current of the generator ie somewhere around 10x the rated current long enough to trip the main breaker on the generator. For this reason, even on rental generators a sliding bar or removable bus bar section is typically used. I’ve seen a (very) large breaker style contactor used but never a switch as it has no withstand rating.
 

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,309
Location
Dutzow Missouri
This sound like a commercial enterprise and no place for amateurs when you are mixing electricity water and the lives of others for profit.

I think the smart move would be to make the generator stationary and hard wire it to a transfer switch so there is zero chance for it to be miss connected in any way.





Walta
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Got a 50KW single phase generator we put it in an enclosed trailer. The use of this generator has 2 purposes. 1. power up small marina during storms. 2. Use as a portable generator. Will be stored off site.

The generator will plug into the buildings transfer switch via a pin and sleeve connector and will be a floating neutral. Inside the trailer we have a a small breaker panel. when used as a stand alone in the field we now need to bond. My thought was to use a switch to bond when used for this purpose and post clear instructions for use. any thoughts on this setup?
so the TS is NOT switching the neutral?
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
When using this generator in stand alone, then this panel must be bonded but not when connected to the building.
correct. standalone needs bond for short circuit and ground fault pathway to allow breakers to trip. when connected to building electrical system without a switched neutral, needs to be isolated as you dont want neutral bonded in 2 places
 