Generator hook-up on power pole

Ramper

Well-known member
Joined
Nov 30, 2010
Messages
1,484
Location
Southern MN
We live on a "farm" meaning the power that comes down out drive ONLY services our property. It splits off sending 100 to the house, 200 to the house and 100(or maybe 200) to the machine shed. We just got a 7000W generator that we would like to hook up to be sure our well pump runs and some other things

Is it possible to hook-up AT THE POLE? That seems like the easiest place. We would need a male hook-up box and a transfer switch. Would the transfer switch have to be rated for 200 amps? We are thinking (could be wrong) that adding wiring to our home would cost more than dealing with the transfer before entering the house.

We had out home built in 2009 and should've had an inlet installed then :(
 
To avoid these ads, REGISTER NOW!

NWOhioChevyGuy

Well-known member
Joined
Feb 20, 2007
Messages
1,924
Location
Buckeye Hill (Morenci, MI)
Yes it is possible I did it just that way. Bought meter / manual transfer switch from my electrical supplier - says property of Consumers Energy right in the box cover. (however I had to purchase it and have it installed)


IMG_2282.jpgIMG_2283.JPG


NWOHIOCHEVYGUY

Still dreaming
 
Last edited:

Eric29

Well-known member
Joined
Apr 18, 2008
Messages
499
Location
Western NY
Generlink makes automatic switches that install behind a meter. When you energize them with a generator, they disconnect from the utility line and feed the generator power to your main panel.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
Yes it is possible I did it just that way. Bought meter / manual transfer switch from my electrical supplier - says property of Consumers Energy right in the box cover. (however I had to purchase it and have it installed)


IMG_2282.jpgIMG_2283.JPG


NWOHIOCHEVYGUY

Still dreaming

Does that meter panel have breakers/main disconnects in it?

Generlink makes automatic switches that install behind a meter. When you energize them with a generator, they disconnect from the utility line and feed the generator power to your main panel.

NEC code requires generators with ATS to be sized for the entire load or have load shedding capabilities...

That gets expensive QUICK...
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,114
Location
SE MI
We live on a "farm" meaning the power that comes down our drive ONLY services our property. It splits off sending 100 to the house, 200 to the house and 100(or maybe 200) to the machine shed. We just got a 7000W generator that we would like to hook up to be sure our well pump runs and some other things. Is it possible to hook-up AT THE POLE?

It could be not too expensive or it could be difficult.

When you say it "splits off", I am assuming there is load center (like owned by the OP) on the pole with at a main and at least 3 breakers. You need a 4th 2-pole breaker and an interlock kit.

Even if you have to change the load center, using an interlock kit is probably cheaper than using DPDT "transfer" safety switch in front of the existing load.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,114
Location
SE MI
Yes it is possible I did it just that way. Bought meter / manual transfer switch from my electrical supplier - says property of Consumers Energy right in the box cover. (however I had to purchase it and have it installed)

Where is the auxiliary feed ? That is basically a generator interlock on steroids with a built in meter socket. Simple and straight forward.
 
Last edited:
OP
R

Ramper

Well-known member
Joined
Nov 30, 2010
Messages
1,484
Location
Southern MN
I have my electrician and the Electric CO electrician looking into it. If they come back with a huge price tag, we will explore other options. We got the generator fora good price, so we want to do it right, but don't want to spend too much money.

The generator is a Reddy 7000Watt with a 13 hp Honda engine. We picked it up at an auction ($190) and when we got it home it fired right up (electric start). We want to avoid extension cords (not sure how that would hook up to the well.

I was not able to take pics last night. There is a "breaker box" at the well as well. We could run the well before the house was built (the old house burnt down). Maybe we could hook the generator to the well and then run extension cords to the house for other needs.
 

NWOhioChevyGuy

Well-known member
Joined
Feb 20, 2007
Messages
1,924
Location
Buckeye Hill (Morenci, MI)
Where is the auxiliary feed ? That is basically a generator interlock on steroids with a built in meter socket. Simple and straight forward.



View attachment 1

This panel feeds both my garage & house, feed to house exits backside of box left side and garage feed exits left side.

This picture is before I had the generator leads ran but they now come in the bottom of the box (smaller conduit) to the breaker on right locked out in the picture.



NWOHIOCHEVYGUY

Still dreaming
 

Attachments

  • IMG_2289.JPG
    IMG_2289.JPG
    131 KB · Views: 80

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
Is the model number of that Milbank panel visible? Noticed there are two Zinsco knockoff breakers and what looks like a interlock on them
 

larry_g

Well-known member
Joined
Apr 28, 2007
Messages
16,873
Location
oregon
The generator is a Reddy 7000Watt with a 13 hp Honda engine. We picked it up at an auction ($190) and when we got it home it fired right up (electric start). We want to avoid extension cords (not sure how that would hook up to the well.

I was not able to take pics last night. There is a "breaker box" at the well as well. We could run the well before the house was built (the old house burnt down). Maybe we could hook the generator to the well and then run extension cords to the house for other needs.

I would suggest that you do some close checking. That generator may not be able to start your well pump. Motors have large inrush current and some generators cannot handle that. I know my old 3/4 hp well pump would not run off of a 5000 watt generator. My new well pump with the VFD on it will run just fine because it does not have the inrush like a direct connected motor will.

lg
no neat sig line
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,710
Location
NW Iowa
A lot of farm or acreage services use pole top or grade level disconnects that already have generator lugs from the factory. In recent years the meter/main setup has become more popular, they do not have this provision. Some can be set up with an interlock like nwohiochevyguy.
 
OP
R

Ramper

Well-known member
Joined
Nov 30, 2010
Messages
1,484
Location
Southern MN
A lot of farm or acreage services use pole top or grade level disconnects that already have generator lugs from the factory. In recent years the meter/main setup has become more popular, they do not have this provision. Some can be set up with an interlock like nwohiochevyguy.

I have an email in to the Electric Coop and they are going to check for me. There is a large box below the meter, but it has a wire tag on it. I assume that I can not open it up and look inside.
 
To avoid these ads, REGISTER NOW!

yeldogt

Well-known member
Joined
Jan 2, 2012
Messages
18,184
Around me the EL CO will not allow you to place items on their pole. No problem on a residential pole owned by you.

The rules when using a manual transfer differ greatly vs an automatic setup. They seem to be designed for grid safety/ best practices -- there is an assumption that you will eliminate any overload condition that would fry your generator.

Auto transfer situation needs to insure generator capacity for any and all load when it switches over.

You would need to make sure of the load prior to switching over
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,710
Location
NW Iowa
I have an email in to the Electric Coop and they are going to check for me. There is a large box below the meter, but it has a wire tag on it. I assume that I can not open it up and look inside.

If it has a handle of the side and says auxiliary then it already is a transfer switch.

No doubt your co-op will let you know what you have but for conversations sake a couple pics would help, you did promise them after all...
 

Eric29

Well-known member
Joined
Apr 18, 2008
Messages
499
Location
Western NY
I didn’t know that. When my son was young, he had a medical condition and we needed to make sure that we had some power to the house if the power went out for a reasonably long period of time. The electric company installed a generlink behind the meter, even though I just had a 4000 watt generator.

Does that meter panel have breakers/main disconnects in it?



NEC code requires generators with ATS to be sized for the entire load or have load shedding capabilities...

That gets expensive QUICK...
 

Bretny

Well-known member
Joined
Jul 31, 2017
Messages
3,918
Location
Dutchess county NY
It looks like you alreaty have a interlock and unused breaker behind it. Notice the two unused lugs under the interlock. Look up the specs on that model electrical box.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,994
Location
Modesto, CA
It looks like you alreaty have a interlock and unused breaker behind it. Notice the two unused lugs under the interlock. Look up the specs on that model electrical box.

Youre confusing someone else's pictures for the OP's.

OP hasnt provided any pictures.
 
OP
R

Ramper

Well-known member
Joined
Nov 30, 2010
Messages
1,484
Location
Southern MN
Just got the quote back from the electrician. $325 installed (including permit) for a 30 amp inlet. Would it make sense to install a larger inlet (say 50 amp) NOW to allow for future upgrades?
 

slow

Well-known member
Joined
Feb 26, 2006
Messages
2,596
Location
near Orlando
how large do you ever see having on a portable generator? Personally, I am doing a 50 amp inlet on my house, but I've got a 15Kw Generac portable generator (way overkill for my needs, but should run the whole house with AC)
 
OP
R

Ramper

Well-known member
Joined
Nov 30, 2010
Messages
1,484
Location
Southern MN
My thoughts are that we built this house 8 years ago and plan to live the REST of lives here. If the cost is not too much more, we should put in the MAXIMUM that we might ever need. This is to be hooked up to a portable generator. Right now we have a 7000W unit and might never upgrade, but if we did we might want the ability to without rewiring. I assume the wire length will be minimal (as the inlet will be on the power pole BEFORE entering the house), so the upgraded wire and inlet should not cost TOO MUCH more.
 
OP
R

Ramper

Well-known member
Joined
Nov 30, 2010
Messages
1,484
Location
Southern MN
The bid says:
Install 30 Amp 125/250 volt generator inlet at pole site disconnect/transfer switch
Note: Your pole site disconnect/transfer switch will allow you to operate as a generator transfer.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,447
Location
Richmond, VA
The bid says:
Install 30 Amp 125/250 volt generator inlet at pole site disconnect/transfer switch
Note: Your pole site disconnect/transfer switch will allow you to operate as a generator transfer.

30 amp is what most portable generators plug into. Unless you need more in an outage, I'd stick with 30 as the cords are cheaper and it is what is on most generators
 

slow

Well-known member
Joined
Feb 26, 2006
Messages
2,596
Location
near Orlando
Ask for the price difference, it should not be much to upgrade, but 50 amp inlet and cords are about double the 30 amp versions.
 
OP
R

Ramper

Well-known member
Joined
Nov 30, 2010
Messages
1,484
Location
Southern MN
We would be able to set the generator within feet of the inlet (short cord). The electrician said we could do that but would have to make an adapter cord for the generator.

The generator uses a L14-20P or L14-30P. I would just need to make a cord that was L-14-30P on one side a L14-50R on the other end
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,447
Location
Richmond, VA
Just got the quote back from the electrician. $325 installed (including permit) for a 30 amp inlet. Would it make sense to install a larger inlet (say 50 amp) NOW to allow for future upgrades?

I don't even think i could get an electician to open my panel for that little around here.
 

slow

Well-known member
Joined
Feb 26, 2006
Messages
2,596
Location
near Orlando
I don't even think i could get an electician to open my panel for that little around here.

I agree, I have been looking for one to do my install just so it is legal and even having the parts, most want a day labor to come out. I need to find the small guy hungry for business.
 