Hi,
I am installing a Kohler 14RESAL-200 generator with an ATS switch.
I need to run yellow PE pipe to the generator and have some questions.
I hope someone can help me with this. Currently I have a propane tank
next to our shed. The tank is connected to the pool heater and a gas stove in the house.
I am planning on putting in a another PE riser next to the gas stove connection outside to the house. The current connection is 25 feet from the propane tank. The generator will be another 30 feet from the gas stove connection. The installation manual for the generator specifies that for each elbow I need to add 8 ft to the total length of the pipe.
I calculated the length of the pipe from the generator to propane tank to be
90ft (including the elbows).
The manual specifies 3/4" pipe for 50ft and 1" pipe for 100ft.
Does this mean I can use 3/4" pipe?
Second question:
There are two options on how to make the connection. I can use a PE tee
inside the ground so that one pipe goes in, one goes to the stove(using a riser) and one goes to the generator OR Use a riser to come out of the ground to black pipe above ground and back to PE pipe with another riser into the ground to the generator.
I have experience running the black pipe but not a lot of experience with PE.
Any suggestions?
Maximum BTU per hour for the generator is 203,000.
Fuel supply pressure
kPa (in. H2O) 1.7--2.7(7--11)
Thank you.
Victor
I am installing a Kohler 14RESAL-200 generator with an ATS switch.
I need to run yellow PE pipe to the generator and have some questions.
I hope someone can help me with this. Currently I have a propane tank
next to our shed. The tank is connected to the pool heater and a gas stove in the house.
I am planning on putting in a another PE riser next to the gas stove connection outside to the house. The current connection is 25 feet from the propane tank. The generator will be another 30 feet from the gas stove connection. The installation manual for the generator specifies that for each elbow I need to add 8 ft to the total length of the pipe.
I calculated the length of the pipe from the generator to propane tank to be
90ft (including the elbows).
The manual specifies 3/4" pipe for 50ft and 1" pipe for 100ft.
Does this mean I can use 3/4" pipe?
Second question:
There are two options on how to make the connection. I can use a PE tee
inside the ground so that one pipe goes in, one goes to the stove(using a riser) and one goes to the generator OR Use a riser to come out of the ground to black pipe above ground and back to PE pipe with another riser into the ground to the generator.
I have experience running the black pipe but not a lot of experience with PE.
Any suggestions?
Maximum BTU per hour for the generator is 203,000.
Fuel supply pressure
kPa (in. H2O) 1.7--2.7(7--11)
Thank you.
Victor