Generator Problem

Lucid Moments

Well-known member
Joined
Aug 9, 2015
Messages
1,775
Location
Gainesville, Ga
We had a little thunderstorm here this evening that knocked power out for several hours. Long enough for me to fire up my generator. The generator is a Predator 9kw starting and 7250 running watts. Unfortunately when I fired it up and plugged in the 240 to the house there was no joy. It was running fine, and I plugged a heat gun into the 120 outlet and that worked, but no 240. I didn't try to diagnose it tonight since it was dark in the shop so where can I start looking tomorrow?
 
To avoid these ads, REGISTER NOW!
OP
L

Lucid Moments

Well-known member
Joined
Aug 9, 2015
Messages
1,775
Location
Gainesville, Ga
There are actually 4 120 outlets on the generator. I did not think to check any more than one though. Power is back on now of course so I will check that tomorrow.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,070
Location
NJ
  1. Stop gen.
  2. Unplug cable.
  3. Make sure all cb's on gen are reset. Check voltages at gen, 120-Neutral, 120-grd, 240-> L1 - L2. Plug in any loads at gen to confirm ok.
  4. Plug in cable at gen and check for voltages at receptacle end....120-Neutral, 120-grd, 240-> L1 - L2.
  5. Plug in cable at Power Inlet box (PIB). Start gen.
  6. Flip cb interlock so panel is running on gen power.
  7. Check voltages at backfed interlock cb. 120-Neutral, 120-grd, 240-> L1 - L2.
Edit: OP replied while typing.

First off - is the gen rated for - 120/240 output?
What recept on the gen is your cable plugged into? Is it 120/240V L14-30R twist-lock outlet?
Is this first use of gen with this connection or has it worked before now?
 
Last edited:
To avoid these ads, REGISTER NOW!
OP
L

Lucid Moments

Well-known member
Joined
Aug 9, 2015
Messages
1,775
Location
Gainesville, Ga
  1. Stop gen.
  2. Unplug cable.
  3. Make sure all cb's on gen are reset. Check voltages at gen, 120-Neutral, 120-grd, 240-> L1 - L2. Plug in any loads at gen to confirm ok.
  4. Plug in cable at gen and check for voltages at receptacle end....120-Neutral, 120-grd, 240-> L1 - L2.
  5. Plug in cable at Power Inlet box (PIB). Start gen.
  6. Flip cb interlock so panel is running on gen power.
  7. Check voltages at backfed interlock cb. 120-Neutral, 120-grd, 240-> L1 - L2.
Edit: OP replied while typing.

First off - is the gen rated for - 120/240 output?
What recept on the gen is your cable plugged into? Is it 120/240V L14-30R twist-lock outlet?
Is this first use of gen with this connection or has it worked before now?
The generator has both 120 and 240 outlets so I guess it is rated for both. I plug the cable into the single 240 outlet and yes it is a twist lock outlet. I have had the generator for a few years and used it previously with everything the same as it is now and had no issues.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,096
Location
Modesto, CA
Did you use a multi-meter to check for voltage at the 240v receptacle?

How are you connecting the generator to the house?
 